Hi Mike
Thank you very much for your answer.
I cannot find 'max figures shadow field in 'shadow
calculations' object. It has only 'periods for
calculations' field. I use 1.4 version.
--- "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> You may increase the limit for this using the
> SHADOWING CALCULATIONS object.
> The second field "Max_figures_shadow" defaults to
> 15000. I would suggest
> increase the limit in small increments of 1000 or
> 2000 just until the error
> goes away.
>
> Mike
>
>
> On 15 Feb 2008 at 5:48, neslihan turkmenoglu wrote:
>
> > hi
> > Although I used
> > 'DIAGNOSTICS,DoNotMirrorDetachedShading', My
> > simulation gives warning as;
> >
> > Too many figures in shadow overlap errors
> occuring...
> > ************* These occur throughout the year
> and
> > may occur several times for the same surfaces. You
> may
> > be able to reduce them by adding
> > DIAGNOSTICS,DoNotMirrorDetachedShading;
> > *************
> > ** Warning ** Too many figures in a shadow
> overlap
> > ** ~~~ ** Overlapping figure=Mir-PAR
> KONSOL-8,
> > Surface Class=[Shading]
> > ** ~~~ ** This error occurred 2 times.
> > ** ~~~ ** Figure being
> > Overlapped=Mir-YUZEYPARALEL-11, Surface
> > Class=[Shading]
> >
> > How can I solve it?
> > thank you very much.
> >
> >
> >
> >
>
__________________________________________________________________________
> > __________
> > Be a better friend, newshound, and
> > know-it-all with Yahoo! Mobile. Try it now.
> >
>
http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
>
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any
> files to the appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open
> EPlusMainMenu.pdf under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
>
>
>
========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
____________________________________________________________________________________
Be a better friend, newshound, and
know-it-all with Yahoo! Mobile. Try it now. http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/