Re: [EnergyPlus_Support] Re: Limited Cooling Capacity



Well, that's certainly a reasonable thing to want to do. And it would be
nice to have an ideal air conditioner to do it - but we don't have one.

The only thing I can think of doing is to use a window AC with a DX
coil (Coil:DX:CoolingBypassFactorEmpirical) and make the 2 capacity
modifier curves constants.

Fred Buhl

Florian Stift wrote:
> Fred,
>
> Thanks for your quick answer!
>
> My problem is that I want to get the air temperatures of a zone with 
> a limited cooling capacity from any ideal system.
> I do not need to define any supply air temperatures or maximum flow 
> rates.
>
> Basically I just want to limit the cooling capacity to e.g. 2kW, to 
> examine the resulting zone air temperatures. I used to use BLAST, 
> where it was quite easy to do that (limit the cooling capacity in the 
> controls tab). 
>
> Do you have any idea how to simulate that within EnergyPlus?
>
> Your help is greatly appreciated.
>
>
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Fred Buhl <wfbuhl@...> 
> wrote:
>   
>> Florian,
>>
>> Since one  can't  set the cooling  capacity of Purchased Air  
>>     
> directly,  
>   
>> (one  can  only  set
>> the maximum flow rate) I assume you are comparing "Purchased Air 
>> Sensible Cooling Rate"
>> with "Zone/Sys Sensible Cooling Load". "Zone/Sys Sensible Cooling 
>>     
> Load" 
>   
>> is calculated
>> after the zone temperature is updated at the end of the HVAC 
>>     
> timestep; 
>   
>> "Purchased Air Sensible Cooling Rate"
>> is calculated using the zone (or return) temperature befor the 
>>     
> update. 
>   
>> If the zone temperature is
>> tightly controlled, there will be no difference. If the zone 
>>     
> temperature 
>   
>> is rising, the zone load
>> will be larger than the Purchased Air output.
>>
>> Fred Buhl
>>
>> Florian Stift wrote:
>>     
>>> I am interested in the air temperatures of a zone in response to 
>>>       
> a 
>   
>>> limited cooling capacity. I don't want to take any system loads 
>>>       
> into 
>   
>>> account.
>>>
>>> When limiting the cooling capacity using the Purchased Air 
>>>       
> Option, the 
>   
>>> air temperature exceeds its setpoints as I supposed but 
>>>       
> the "Zone/Sys 
>   
>>> Sensible Cooling Load" is higher than the limited cooling 
>>>       
> capacity. How 
>   
>>> can simulation results outrun the cooling capacity entered?
>>>
>>> Thanks for your help!
>>>
>>>  
>>>
>>>
>>>
>>>
>>>
>>> The primary EnergyPlus web site is found at:
>>> http://www.energyplus.gov
>>>
>>> The group web site is:
>>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>>
>>> Attachments are not allowed -- please post any files to the 
>>>       
> appropriate folder in the Files area of the Support Web Site.
>   
>>> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
>>>       
> under the Documentation link and press the "search" button.
>   
>>>  
>>> Yahoo! Groups Links
>>>
>>>
>>>
>>>
>>>       
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>  
> Yahoo! Groups Links
>
>
>
>   


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/