From the Input Output Reference for COMPACT HVAC:SYSTEM:VAV "Heat
Recovery Type": If heat recovery is specified, then a value must be
entered in the Minimum Outside Air Flow Rate field, because heat
recovery equipment is not yet autosizable.
This will be autosizeable in v2.2.
Mike
deserteagle_zhou wrote:
> Hello all£¬
>
> I added Heat Recovery type as well as Sensible/latent effectiveness
> into the COMPACT HVAC:SYSTEM:VAV object. Then the program gave fatal
> errors and terminated the calculation. I input related outside air flow
> rate in the expanded file, but things held the same. It seems a bug in
> the compact object.
>
> Would someone take a look at the uploaded file named "compact ERV"?
> Thank you in advance.
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/