Re: [EnergyPlus_Support] cp values input



The model uses linear interpolation to calculate CP values. The difference 
of wind direction between #i and #i+1 is a denominator in the linear 
interpolation. When the two values are the same, "divided zero" occurs. That 
is why two repeated values of wind direction used in the 
AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE COEFFICIENT ARRAY object are not 
allowed.

Lixing

----- Original Message ----- 
From: "neslihanturkmenoglu" <neslihanturkmenoglu@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Wednesday, March 12, 2008 11:16 AM
Subject: [EnergyPlus_Support] cp values input


>
> Hi Lixing
> I used my own cp values as input which acted on front an back
> surfaces with a wind direction of 180.  Program didn't accept
> repeated values or one aveage value so I wrote the angles with 30
> range. Now I get no errors but I have no idea about what I did. Can
> You explain how it works.
> Thank you very much.
>
>
> !-   ===========  ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:WIND
> PRESSURE COEFFICIENT ARRAY ===========
>
> AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE COEFFICIENT ARRAY,
>    nesli basinc,            !- WPC Array Name
>    10.0,                    !- Reference Height for WPC Data {m}
>    0,                       !- Wind Direction #1 {deg}
>    30,                      !- Wind Direction #2 {deg}
>    60,                      !- Wind Direction #3 {deg}
>    90,                      !- Wind Direction #4 {deg}
>    120,                     !- Wind Direction #5 {deg}
>    150,                     !- Wind Direction #6 {deg}
>    180,                     !- Wind Direction #7 {deg}
>    210;                     !- Wind Direction #8 {deg}
>
>
> !-   ===========  ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:WIND
> PRESSURE COEFFICIENT VALUES ===========
>
> AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE COEFFICIENT VALUES,
>    nesli basinc,            !- AirflowNetwork WPC Array Name
>    front node ,             !- External Node Name
>    1.019,                   !- WPC Value #1 {dimensionless}
>    0.974,                   !- WPC Value #2 {dimensionless}
>    1.056,                   !- WPC Value #3 {dimensionless}
>    0.983,                   !- WPC Value #4 {dimensionless}
>    0.919,                   !- WPC Value #5 {dimensionless}
>    0.753,                   !- WPC Value #6 {dimensionless}
>    0.694,                   !- WPC Value #7 {dimensionless}
>    0.563;                   !- WPC Value #8 {dimensionless}
>
> AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE COEFFICIENT VALUES,
>    nesli basinc,            !- AirflowNetwork WPC Array Name
>    back node,               !- External Node Name
>    -.662,                   !- WPC Value #1 {dimensionless}
>    -.713,                   !- WPC Value #2 {dimensionless}
>    -.759,                   !- WPC Value #3 {dimensionless}
>    -.673,                   !- WPC Value #4 {dimensionless}
>    -.725,                   !- WPC Value #5 {dimensionless}
>    -.674,                   !- WPC Value #6 {dimensionless}
>    -.701,                   !- WPC Value #7 {dimensionless}
>    -.639;                   !- WPC Value #8 {dimensionless}
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate 
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the 
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
> 



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/