RE: [EnergyPlus_Support] Connector list for Air Primary Loop
Unless you have a dual duct system, you don't really need a Connector
List. That field can be left blank in the Air Primary Loop.
The Zone Splitter is on the demand side of the air loop and only needs
to be referenced in the Zone Supply Air Path. Similarly the Zone Mixer
is referenced in the Zone Return Air Path.
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of JV Dirkes II
Sent: Friday, March 14, 2008 5:06 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Connector list for Air Primary Loop
Dear EPlus support team,
Will someone please explain:
The Air Primary Loop asks for a Connector list.
The Connector List object asks for the types of components, and
Splitter and Mixer are the only acceptable choices.
When I use the ZONE Splitter and ZONE mixer names within the Connector
List, I get a Severe error.
What am I supposed to do?
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/