RE: [EnergyPlus_Support] Re: No matching inlet or exhaust nodes....
The BRANCH input object is not used or needed on the demand side of air
system loops. Try deleting it. If that doesn't fix it, then please up
load the input file.
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of JV Dirkes II
Sent: Monday, March 17, 2008 12:57 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: No matching inlet or exhaust nodes....
Dear EPlus support,
In hopes of getting a response for this post, I'll re-phrase one of
the questions with more detail...
My system model has a constant volume fan and each zone has a single
Branch with a reheat coil. When I defined this as follows, I receive
the Warning shown below (which does NOT occur when running
"TermReheatZoneExh.idf" from the Example files, even though I've tried
to duplicate the node occurrences):
ZONE EQUIPMENT LIST,
ZoneEqList_GardenLevel, !- Name
AIR DISTRIBUTION UNIT, !- KEY--Zone Equipment Type 1
DirAir_Zone1_AH1, !- Type Name 1
1, !- Cooling Priority 1
1, !- Heating Priority 1
ZONE EXHAUST FAN, !- KEY--Zone Equipment Type 2
ExhFan_Zone1_AH1, !- Type Name 2
2, !- Cooling Priority 2
2; !- Heating Priority 2
AIR DISTRIBUTION UNIT,
DirAir_Zone1_AH1, !- Air Distribution Unit Name
NodeOut_Rht_GardenLevel, !- Air Dist Unit Outlet Node Name
SINGLE DUCT:CONST VOLUME:REHEAT, !- KEY--System Component Type 1
RhtCTRL_GardenLevel; !- Component Name 1
SINGLE DUCT:CONST VOLUME:REHEAT,
RhtCTRL_GardenLevel, !- Name of System
SchCpct_AlwaysOn, !- System Availability schedule
NodeOut_Rht_GardenLevel, !- Unit Air Outlet Node
NodeOut_DirAir_GardenLevel, !- Unit Air Inlet Node
Autosize, !- Maximum air flow rate {m3/s}
, !- Control node
COIL:GAS:HEATING, !- Reheat Component Object
RhtCoil_GardenLevel, !- Name of Reheat Component
, !- Max Reheat Water Flow {m3/s}
, !- Min Reheat Water Flow {m3/s}
0.001; !- Convergence Tolerance
BRANCH,
Branch_Rht_GardenLevel, !- Branch Name
Autosize, !- Maximum Branch Flow Rate {m3/s}
COIL:GAS:HEATING, !- Comp1 Type
RhtCoil_GardenLevel, !- Comp1 Name
NodeOut_DirAir_GardenLevel, !- Comp1 Inlet Node Name
NodeOut_Rht_GardenLevel, !- Comp1 Outlet Node Name
ACTIVE; !- Comp1 Branch Control Type
COIL:Gas:Heating,
RhtCoil_GardenLevel, !- Coil Name
SchCpct_HtgAvail_AH1, !- Available Schedule
0.8, !- Gas Burner Efficiency of the Coil
Autosize, !- Nominal Capacity of the Coil {W}
NodeOut_DirAir_GardenLevel, !- Coil_Air_Inlet_Node
NodeOut_Rht_GardenLevel, !- Coil_Air_Outlet_Node
, !- Coil_Temp_Setpoint_Node
50, !- Parasitic Electric Load {W}
HtgCoil_ PLF-FPLR_AH1, !- Part load fraction correlation
0; !- Parasitic Gas Load {W}
** Warning ** Node used as an inlet more than once:
NODEOUT_DIRAIR_GARDENLEVEL
** ~~~ ** Used by : BRANCH, name=BRANCH_RHT_GARDENLEVEL
** ~~~ ** as inlet for: COIL:GAS:HEATING,
name=RHTCOIL_GARDENLEVEL
** ~~~ ** and by : SINGLE DUCT:CONST VOLUME:REHEAT,
name=RHTCTRL_GARDENLEVEL
** ~~~ ** as inlet for: COIL:GAS:HEATING,
name=RHTCOIL_GARDENLEVEL
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> , "JV Dirkes II"
<jvd2pe@...>
wrote:
>
> Dear EPlus Support,
>
> I have an assortment of Severe errors which are described as:
> "ZoneExhaust node did not find a matching inlet node..." or
> "Inlet node did not find an appropriate matching 'outlet' node."
>
> For my exhaust fan, I have defined the CONTROLLED ZONE EQUIP
> CONFIGURATION exhaust node the same as the Exhaust Fan inlet node. I
> do not understand what a "matching inlet node" is supposed to be.
> Please help!
>
> Similarly, I do not understand what a matching 'outlet' node is. The
> error message refers in several cases to the node which is the return
> air inlet to an Outside Air Mixer. Another case is an inlet node to a
> chilled ware pump on the supply side of a Plant Loop.
>
> Thanks for your help!
>
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/