Re: [EnergyPlus_Support] WINDOWS 6 Import Procedure
If there is only one glazing system in the window construction that you
are importing from the WINDOW5/6 data file, then EnergyPlus will use the
dimensions input for the window in your IDF. However, these are
considered the "rough opening" dimensions, and so the dimensions of the
frame (which is included in the WINDOW5/6 data file) will be subtracted
from the rough opening to get the glazed area of the window.
The warning about >10% variation in size is to alert you to the fact
that the overall window system performance characteristics reported by
WINDOW5/6, for the dimensions input in that program, may be different
from those calculated by EnergyPlus for the dimensions given in your IDF
input.
Rob
========
Nuno Costa Brandão wrote:
> Dear All,
>
> I´m using "Windows 6 research version" to import a triple low-e
> glazing for my simulation. I´m not using its shading import
> capabilities, I´m only importing the glazing system. I´m a little bit
> unsure about the EnergyPlus calculations using the dat file from
> "Window 6".
>
> I´m using only one glazing system, and as its said in the I/O
> reference, EPlus ignores the W6 dimensions and uses the one´s from the
> original idf. However there is a warning message about the 10%
> dimension difference issue. In the HTML Envelope Summary report file
> from the idf that uses the W6 glazing, the fenestration areas are
> different from the original idf file using another glazing system. I'm
> a little bit confused... From which I understood, I suppose EPlus
> would use the original idf window dimensions to calculate heat
> transfer??? I´m using a frame with thermal break.
>
> Can you give me some guidance help?
> Thanks
> Nuno
>
>
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/