Re: [EnergyPlus_Support] Heat exchanger smart bypass control
I think you should be able to model this with EnergyPlus.... at least
the cooling part.
As described in the documentation, the Heat Exchanger:Generic:Air To Air
object is able to "suspend heat exchange" (e.g., bypass the airflow) for
the purpose of providing free cooling operation in the absence
of a conventional air-side economizer (i.e., specify BYPASS in the
EconomizerChoice field of the Controller:Outside Air object). Set the
field "ReturnAirTempLimit" in the Controller:Outside Air object to
RETURN AIR TEMP LIMIT.
> anarui.oliveira wrote:
>
>> I was looking for a Heat Exchanger bypass control that would implement
>> the algorithm:
>>
>> If (Cooling) AND (Outdoor Temperature < Return Temperature) -> Bypass
>> If (Heating) AND (Outdoor Temperature > Return Temperature) -> Bypass
>>
>> instead of controlling based on hard temperature limits.
>>
>> E+ doesn't currently have this kind of control, does it?
>>
>> Thank you,
>> Ana.
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/