All of my air handlers have System Sizing results (from the ...Ssz.csv
file) similar to what I've shown below. Since I'm less familiar with
the SI units, I've converted some of the values to US measures.
AIRLOOP_AH1:Des Cool Mass Flow [kg/s]
3.10E+00 (coinicident)
3.23E+00 (non-coincident; ~5680 cfm)
AIRLOOP_AH1:Des Sens Cool Cap [W]
5.25E+04
5.25E+04 (~179.3 MBH)
Delta T: ~29.2F
I have a question about the delta T value. My System Sizing object
sizes on 'noncoincident' 'sensible' load, defines the 'Central cooling
design supply air temperature (deg C)' as 12.8C. The Cooling setpoint
is 23.9C. Thus the Delta T is 11.1C (~20F). Why does the System
Sizing.csv file indicate a delta T dramatically higher than 11C / 20F?
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/