Re: [EnergyPlus_Support] Re: InitializeRootFinder: error
The intent was to permit non-zero minimum values for the control valve flow,
for the reason you have given. We'll work to get it working againg.
Fred Buhl
JV Dirkes II wrote:
> Thanks for the details, Brent.
>
> For the reasons cited below (real control valves often unable to close
> fully), I think it will be of practical value to model non-zero
> minimum flows, so I vote for the change!
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent"
> <brent_griffith@...> wrote:
>
>> I am afraid it may not be possible to use a non-zero min actuated flow
>> in version 2.1. It's the Xmax that is the problem. This value appears
>> to be getting set to zero by the actuated node's value for
>> MassFlowRateMaxAvail (these can be reported with
>> DisplayAdvancedReportVariables diagnostics). I suspect it may be an
>> internal problem in how the component simulation is interacting with
>> plant loop; this is something we are currently working on fixing for the
>> next release. Thanks for bringing this to our attention.
>>
>>
>>
>> The difference in magnitude in the values here is the difference between
>> volume flow rate (input) and mass flow rate (error message).
>>
>>
>>
>>
>>
>>
>>
>> ________________________________
>>
>> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
>> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of JV Dirkes II
>> Sent: Thursday, April 03, 2008 9:09 AM
>> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>> Subject: [EnergyPlus_Support] Re: InitializeRootFinder: error
>>
>>
>>
>> Thank you TJ!
>>
>> Do you know why the small value I used causes this problem? and is
>> there a way to use a non-zero value which will not cause the error?
>>
>> I used a non-zero value because many control valves cannot shut off
>> completely due to improper actuator selection, and I wanted to include
>> the effects of that in the simulation.
>>
>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
>> <mailto:EnergyPlus_Support%40yahoogroups.com> , "tjutw" <tjutw@>
>> wrote:
>>
>>> I guess you just changed one controller.
>>> In the input file, there are two ""Controller:Simple". You need change
>>> both of them.
>>>
>>> Tj Ywh
>>>
>>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
>>>
>> <mailto:EnergyPlus_Support%40yahoogroups.com> , "JV Dirkes II" <jvd2pe@>
>>
>>> wrote:
>>>
>>>> Dear TJ,
>>>>
>>>> You are correct that my value was .000005 in that field (which is
>>>>
>> not
>>
>>>> the same as indicated by the message!), but I must be missing
>>>> something; changing the value to 0 results in the same error.
>>>>
>>>> Any other insights?
>>>>
>>>>
>>>>
>>>>
>>>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
>>>>
>> <mailto:EnergyPlus_Support%40yahoogroups.com> , "tjutw" <tjutw@> wrote:
>>
>>>>> If you change the "Min Actuated Flow" in the "Controller:Simple"
>>>>> Object from 0.000005 to 0, then the model runs well.
>>>>>
>>>>> Tj Ywh
>>>>>
>>>>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
>>>>>
>> <mailto:EnergyPlus_Support%40yahoogroups.com> , "JV Dirkes II" <jvd2pe@>
>>
>>>>> wrote:
>>>>>
>>>>>> Dear EPlus Forum,
>>>>>>
>>>>>> Can anyone give me a clue what causes the error below? It's the
>>>>>>
>>> only
>>>
>>>>>> error in the .err file.
>>>>>>
>>>>>> Thanks!
>>>>>>
>>>>>> ** Fatal ** InitializeRootFinder: Invalid min/max bounds
>>>>>> XMin=5.000001E-003 must be smaller than XMax=0.000000
>>>>>>
>>>>>>
>>
>>
>>
>>
>> [Non-text portions of this message have been removed]
>>
>>
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/