Re: [EnergyPlus_Support] Re: Setpoint not met during night cycle
It is supposed to run work that way, though as you point out that
it may not make the most sense.. Thanks for solving your own problrm!
Fred
JV Dirkes II wrote:
> Dear E+ Forum,
>
> After experimenting some more, it appears that the SYSTEM AVAILABILITY
> MANAGER:NIGHT CYCLE "Cycling run time" was preventing the zone from
> reaching the setpoint. When I set it for 900s (15 min), it would turn
> the system OFF at the end of that period, even though the setpoint was
> not met. In other words, it came ON for 900s, turned OFF for 900S,
> then ON for 900s , etc.
>
> When I set the "Cycling run time" for 3600s, it operates on a longer
> cycle, which allows the zone to warm properly. Of course the fan runs
> a lot more, too!
>
> I guess I've solved my own problem for now, but still have a question:
>
> 1) Is the SYSTEM AVAILABILITY MANAGER:NIGHT CYCLE supposed to work
> this way? It seems to me that a control system should operate in
> NIGHT CYCLE as long as needed to achieve the setpoint, and then shut
> off. My first understanding of the "Cycling run time" was as a
> MINIMUM run time. That's apparently incorrect, but it seems to be
> more appropriate....
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@...>
> wrote:
>
>> Dear EPlus Forum,
>>
>> Please help me determine why my model maintains proper setpoints
>> during Winter Design Days in the "night" period, but fails to do so on
>> other winter days.
>>
>> During the night, the setpoints are as expected, the system cycles on
>> and off as expected (I'm using a SYSTEM AVAILABILITY MANAGER:NIGHT
>> CYCLE), but the zone temp is much lower than the setpoint (including
>> the thermostat on/off tolerance).
>>
>> I'll upload the file....
>>
>>
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/