[EnergyPlus_Support] Re: temperature gradient
Hi Lixing
I calculated wind speed profile exponent with the values got from
wind tunnel measurements in front of the scale model.
In order to understand, I change the values one by one in weather
station object or site atmospheric variation object, nothing changed
in the results of airflow volume flow rate 2 to 1.
The only change occured when I enter my wind speed profile exponent
to airflow network-site wind conditions object.
I understood that one exponent is for weather site conditions,
the other exponent is for building site conditions.Why is there the
third one with another default value in airflow network site wind
conditions?
when I compare the results of energyplus with my manually calculated
volume flow rates, they are not the same. So in order to define the
wind tunnel conditions in Energyplus, what do you suggest me to do?
And which velocity should I enter to design object wind velocity
field- u mean calculated from measured data in front of the scale
model or the wind tunnel's 2.5 m/s Gradient velocity %10 Motor
velocity.
I hope you answer in a short time.
thank you very much
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>
> Neslihan:
>
> You may use the scale model to get the real size wind profile from
the wind
> tunnel testing data.
>
> I think you may use the default value for tempeature gradient
coefficient. I
> could not find any fields to address velocity gradient. Please
provide
> specific information. For inputs of the WEATHER STATION object, you
may use
> the real size wind profile to generate input values of both fields
of Wind
> Sensor Height Above Groundand Wind Speed Profile Exponent.
>
> Best regards,
>
> Lixing
> ----- Original Message -----
> From: "neslihanturkmenoglu" <neslihanturkmenoglu@...>
> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> Sent: Thursday, April 10, 2008 9:20 AM
> Subject: [EnergyPlus_Support] temperature gradient
>
>
> > hi Lixing
> >
> > thank you very much for your answer. Sorry for disturbing you too
> > much:)But I am in trouble as I try to learn building aerodynamics,
> > energyplus and others at the same time:)
> > Now I have another question.
> > I have velocites measured to a height of 35cm with an interval of
1cm
> > on wind tunnel in front of the model.
> > I want to use these as reference velocities. I think I have to
fill the
> > weather station and site atmospheric variation. I don't have data
of
> > air temperature gradient.
> > So will I write 0 to air temperature gradient coefficient field?
> > How will I enter my own velocity gradient?
> > thank you
> >
> >
> > ------------------------------------
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate
> > folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/