[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Controller actuator error
Loop Demand=89853672305 W ? That's not a large room, it's a small country.
Check that this number is greater than the Load Range Upper Limit
specified in your file.
If so, increase the load range upper limit and the equipment should turn on:
COOLING LOAD RANGE BASED OPERATION,
Central Chiller Only, !- Name
0, !- Load Range Lower Limit 1 {W}
900000, !- Load Range Upper Limit 1 {W}
Cooling Plant; !- Priority Control Equip List Name 1
brian.aldred@xxxxxxxxxxx wrote:
>
> I have an input file which describes a fairly large room served by a
> constant volume A/C system. When run with the two design days, I get
> errors for the controllers as follows:
>
> ** Warning ** No valid range found for Loop Demand=89853672305.89 in
> Load Range Based Operation Scheme=X1:CONTROL.
> ** ~~~ ** All equipment will be turned off. Other cases of this
> condition will not be reported.
> ** ~~~ ** During Warmup, Occurrence info=SUMMERDESIGNDAY, 07/15
> 05:00 - 05:15
> ** Warning ** No valid range found for Loop Demand=-3573128227.79 in
> Load Range Based Operation Scheme=Z1:CONTROL.
> ** ~~~ ** All equipment will be turned off. Other cases of this
> condition will not be reported.
> ** ~~~ ** During Warmup, Occurrence info=SUMMERDESIGNDAY, 07/15
> 08:00 - 08:15
> ** Severe ** FindRootSimpleController: Controller error for
> controller = A10:CONHEAT
> ** ~~~ ** Occurrence info=SUMMERDESIGNDAY, 07/15 07:00 - 07:15
> ** ~~~ ** Controller function is inconsistent with user
> specified controller action = Normal action
> ** ~~~ ** Actuator will be set to maximum action
> ** ~~~ ** Controller control type=Temperature
> ** ~~~ ** Controller temperature set point = 18.00 [C]
> ** ~~~ ** Controller sensed temperature = 16.39 [C]
> ** ~~~ ** Controller actuator mass flow rate set to 3106776.89
> [kg/s]
> ** ~~~ ** Controller actuator temperature = 16.25 [C]
> ** ~~~ ** Note: Chilled water coils should be reverse action
> and the entering chilled
> ** ~~~ ** water temperature (controller actuator
> temperature) should be below the setpoint temperature
> ** ~~~ ** Note: Hot water coils should be normal action and the
> entering hot
> ** ~~~ ** water temperature (controller actuator
> temperature) should be above the setpoint temperature
> ** Severe ** FindRootSimpleController: Controller error for
> controller = A10:CONCOOL
> ** ~~~ ** Occurrence info=SUMMERDESIGNDAY, 07/15 08:00 - 08:15
> ** ~~~ ** Controller function is inconsistent with user
> specified controller action = Reverse action
> ** ~~~ ** Actuator will be set to maximum action
> ** ~~~ ** Controller control type=Temperature
> ** ~~~ ** Controller temperature set point = 18.00 [C]
> ** ~~~ ** Controller sensed temperature = 21.81 [C]
> ** ~~~ ** Controller actuator mass flow rate set to 1104896.15
> [kg/s]
> ** ~~~ ** Controller actuator temperature = 25.25 [C]
> ** ~~~ ** Note: Chilled water coils should be reverse action
> and the entering chilled
> ** ~~~ ** water temperature (controller actuator
> temperature) should be below the setpoint temperature
> ** ~~~ ** Note: Hot water coils should be normal action and the
> entering hot
> ** ~~~ ** water temperature (controller actuator
> temperature) should be above the setpoint temperature
>
> I am struggling to determine the cause (and fix) of this error and would
> like to know if you can give any insights?
>
> As far as I can see, we are specifying everything correctly, and if I
> replicate the same hvac system in another similarly sized room I do not
> get the error. The file has been uploaded as in - controller actuator
> error.idf
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP>
> N6jLN908jlXIXTDGkHxBJGY-Hx941z8oEuIe2cMRFAd5xUcXCp224/_Problem_Submittal
> s/in%20-%20controller%20actuator%20error.idf> in the Files, Problem
> Submittals section.
>
> Any help you can give would be much appreciated.
>
> Please contact us further if you require any additional information or
> assistance.
>
> Brian Aldred
> Software Development
> Tel: 0114 255 6680
> Fax: 0114 255 6638
>
> Hevacomp Ltd is a company registered in England and Wales with company
> number 1523216
> Registered office: Smithywood House, Smithywood Crescent, Sheffield, S8
> 0NU
>
> P Help save paper - do you need to print this email?
>
> [Non-text portions of this message have been removed]
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/