Thanks, Matthew!  I remember now about that prioritization within Zone
Equipment List; we'll see how it works for this situation.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Matthew Flannery"
<matthew.flannery@...> wrote:
>
> Have you tried looking at your zone equipment list?  This only works if
> you're out of compact mode.  In this tab you define your zone heating
> priority for reheat coils and baseboard heaters.
> 
>  
> 
>  
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST ===========
> 
>  
> 
> ZONE EQUIPMENT LIST,
> 
>     Zone_1 Equipment,        !- Name
> 
>     AIR DISTRIBUTION UNIT,   !- KEY--Zone Equipment Type 1
> 
>     Zone_1 Reheat Coil,      !- Type Name 1
> 
>     2,                       !- Cooling Priority 1
> 
>     2,                       !- Heating Priority 1
> 
>     BASEBOARD HEATER:WATER:CONVECTIVE,  !- KEY--Zone Equipment Type 2
> 
>     Zone_1 Baseboard,        !- Type Name 2
> 
>     1,                       !- Cooling Priority 2
> 
>     1;                       !- Heating Priority 2
> 
>  
> 
>  
> 
> Matthew Flannery, LEED A.P.
> 
> Mechanical Engineer
> 
> Buro Happold Consulting Engineers, PC
> 100 Broadway 
> New York, NY 10005
> USA
> 
>  
> 
>  
> 
>  
> 
> ________________________________
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of JV Dirkes II
> Sent: Sunday, April 27, 2008 8:02 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Staging baseboard and reheat coil
> 
>  
> 
> Dear E+ Forum,
> 
> I'm trying to figure out how to make baseboard heating and a reheat
> coil act as Stage 1 and Stage 2 of the zone's heating. Stage 2 (the
> reheat coil) should stay off until the Baseboard (Stage 1) is at full
> capacity.
> 
> Thanks in advance.
> 
>  
> 
> 
> 
> This message has been scanned by MailController -
www.MailController.altohiway.com
> 
> 
> [Non-text portions of this message have been removed]
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/