RE: [EnergyPlus_Support] Staging baseboard and reheat coil



Have you tried looking at your zone equipment list?  This only works if
you're out of compact mode.  In this tab you define your zone heating
priority for reheat coils and baseboard heaters.

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST ===========

 

ZONE EQUIPMENT LIST,

    Zone_1 Equipment,        !- Name

    AIR DISTRIBUTION UNIT,   !- KEY--Zone Equipment Type 1

    Zone_1 Reheat Coil,      !- Type Name 1

    2,                       !- Cooling Priority 1

    2,                       !- Heating Priority 1

    BASEBOARD HEATER:WATER:CONVECTIVE,  !- KEY--Zone Equipment Type 2

    Zone_1 Baseboard,        !- Type Name 2

    1,                       !- Cooling Priority 2

    1;                       !- Heating Priority 2

 

 

Matthew Flannery, LEED A.P.

Mechanical Engineer

Buro Happold Consulting Engineers, PC
100 Broadway 
New York, NY 10005
USA

 

 

 

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of JV Dirkes II
Sent: Sunday, April 27, 2008 8:02 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Staging baseboard and reheat coil

 

Dear E+ Forum,

I'm trying to figure out how to make baseboard heating and a reheat
coil act as Stage 1 and Stage 2 of the zone's heating. Stage 2 (the
reheat coil) should stay off until the Baseboard (Stage 1) is at full
capacity.

Thanks in advance.

 



This message has been scanned by MailController - www.MailController.altohiway.com


[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/