I find the documentation isn't completely clear to me on this point.
So, if I have a zone which, in reality, has only forced exhaust, and
which receives air by pressure difference from an adjacent zone, what
would be the best way to model it, for the purpose of heat balance
and thermal loads calculation?
If I use just the mixing and infiltration objects, is it actually as
if I was continuously increasing the zone air volume? Should I add a
mixing object to extract the correspondent airflow to some dummy zone?
If I implement an exhaust fan, since the mixing object does not use
inlet nodes, I suppose I'll get unbalanced flow errors?...
Thanks again,
Ana.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Edwin Lee"
<leeed2001@...> wrote:
>
> There is also a cross-mixing object, which is described in the
> documentation, that simulates air exchange between two zones, and
therefore
> affects both zones energy balance.
>
> On Mon, Apr 28, 2008 at 9:36 AM, Richard Raustad <RRaustad@...>
> wrote:
>
> > When mixing objects are used, the user is responsible for
accurately
> > predicting the air flow into and out of a zone. Only air entering
a zone
> > is used in the heat balance. Infiltration and mixing (into a
zone) are
> > included in the heat balance predict step (mi and minf in Eng.
Ref. Eq 2
> > and 5) Supply air entering a zone is included in the heat balance
> > correct step (msys in Eng. Ref. Eq 5). The return air leaving the
zone
> > is assumed to be balanced based on the supply and exhaust node
mass flow
> > rates (mixing and infiltration are not included here). You can
read more
> > about the assumptions for balanced flow in the text near these
equations
> > in the Engineering Reference.
> >
> >
> > anarui.oliveira wrote:
> > >
> > > Hi, everyone.
> > >
> > > I think I've read this somewhere, but I can't find it now:
> > >
> > > - When doing the heat Balance for a Zone Air volume that is
receiving
> > > air with a mixing object, does E+ assume that an equal amount
of air is
> > > withdrawn from that zone, for heat balance purposes?
> > >
> > > Thank you in advance,
> > > Ana Rui.
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >
> >
>
>
> [Non-text portions of this message have been removed]
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/