Re: [EnergyPlus_Support] Staging baseboard and reheat coil



Actually I don't think that is correct. The air terminal units are 
treated as zone equipment
just like the baseboards. So which is simulated first in the zone 
equipment simulation?
It is up to you, the user. Look at the Zone Equipment List. For each 
controlled zone, this lists
the units that can act to heat and/or cool the zone. Along with each 
unit there is a cooling
and a heating priority. Making the heating priority of the baseboard 1 
and the terminal unit 2
should cause the baseboard to try to meet the zone heating load first.

Fred Buhl

Richard Raustad wrote:
> The air loops (reheat coils) are simulated first in E+ and zone 
> equipment (baseboards) are simulated next. I know of now way to make the 
> baseboard heaters act as "Stage 1" heating. The closest you could get 
> would be to downsize the reheat coils and allow the baseboard heaters to 
> pick up some of the load.
>
> JV Dirkes II wrote:
>   
>> Dear E+ Forum,
>>
>> I'm trying to figure out how to make baseboard heating and a reheat
>> coil act as Stage 1 and Stage 2 of the zone's heating. Stage 2 (the
>> reheat coil) should stay off until the Baseboard (Stage 1) is at full
>> capacity.
>>
>> Thanks in advance.
>>
>>  
>>     
>
>   


[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/