Re: [EnergyPlus_Support] In the same zone , fan-coil object + exhaust fan



Thank you Fred.


----- Original Message ----
From: Fred Buhl <wfbuhl@xxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Friday, May 16, 2008 7:25:39 PM
Subject: Re: [EnergyPlus_Support] In the same zone , fan-coil object + exhaust fan


Andre:

You can have the 2 objects, but it may not do what you want. The fan 
coil uses a zone inlet node and a zone
exhaust node (to get its zone air). The exhaust fan would use a 
different, separate exhaust node. The program
will complain that the air flow is not balanced, but don't worry about 
that. The fan coil can also draw in outside
air and you can make it 100% outside air if you wish, but you will still 
need that 1st exhaust node (fan coil inlet)
even if it isn't getting any air from it.

Fred Buhl

André Lopes wrote:
> Thank you for your answer.
> I have a zone with the Fan Coil object, and I need to add an exhaust fan to this zone? Can I have the two objects?
> I tried, but I think I can not modify the Controlled Zone Equipment Configuration, because the Fan Coil needs a Return. How can I do it? 
> Regards
> A L
>
> ----- Original Message ----
> From: Richard Raustad <RRaustad@FSEC. UCF.EDU>
> To: EnergyPlus_Support@ yahoogroups. com
> Sent: Friday, May 16, 2008 4:46:49 PM
> Subject: Re: [EnergyPlus_ Support] Objects needed to configure a Zone Supply Fan ?
>
>
> Try using the ventilation object. It's very simple and allows you to 
> schedule outside air and report fan energy.
>
> André Lopes wrote:
> 
>> Hello All
>> I need to know what objects are necessary to configure a Zone Supply fan..
>> This fan is just for one zone (Warehouse) and it uses on his inlet 
>> Outside Air. It works continuously 12h per day
>> Best Regards
>> A L
>>
>>
>> 
>
> 

[Non-text portions of this message have been removed]

 


      

[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/