[EnergyPlus_Support] Re: Variable speed pumps



Thanks, Richard!

I don't look in the Engineering reference often enough; I guess I'll
have to broaden my search technique!

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> Did you miss this equation in the Eng. Ref?
> 
> PartLoadRatio = VolFlowRate / PumpEquip(PumpNum)%NomVolFlowRate
> 
> JV Dirkes II wrote:
> >
> > Dear Eplus Forum,
> >
> > After creating some curve fits for a couple variable speed pump
> > configurations, it occurred to me that I was not really sure what E+
> > thinks is the "PLR". I had assumed it to be the actual load fraction.
> > For a CONSTANT temperature water system, water flow rate will be
> > proportional to load fraction. For a VARIABLE temperature system
> > (e.g., reset by outdoor air temperature), load fraction and water flow
> > rate are NOT proportional.
> >
> > I'm hoping that E+ uses water flow rate as the basis for "PLR". Will
> > someone let me know for sure? Thank you.
> >
> > >From the I/O Reference:
> > FractionFullLoadPower =C1+C2PLR+C3PLR +C4PLR
> >
> >  
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/