[EnergyPlus_Support] Re: Modeling an air handler with a relief fan



Thanks Tj.  I'll try it.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "tjutw" <tjutw@...> wrote:
>
> You can include a relief fan in the outside air system equipment. The
>  relief fan inlet node is the relief air stream node in the "outside
> air mixer" Object.  
>   
> Given the airflow rate of this relief fan is much less than a return
> fan, you can just decrease the fan pressure from the energy use
> prospective.   
> 
> Hope it helps,
> 
> Tj Ywh
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@>
> wrote:
> >
> > Can anyone answer this question?
> > 
> > Thanks!
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@>
> > wrote:
> > >
> > > Dear EPlus Forum,
> > > 
> > > I want to model a relief fan working in concert with an air
handler. 
> > > This is commonly operated like a variable speed exhaust fan which is
> > > placed in the relief airstream of an outdoor air mixer and removes
> > > excess economizer air. 
> > > As a result the fan heat does not go to the return air stream,
and the
> > > airflow rate is often much less than a return fan, since some of the
> > > air exits the building through cracks.
> > > I could not find an example or previous forum discussion which shows
> > > this.  Can anyone give some guidance about how do model this?
> > > 
> > > Thanks!
> > >
> >
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/