Re: [EnergyPlus_Support] Re: Humidifiers
The calculations in the model are all done in terms of mass flow rate
(kg/s). The input
for nominal capacity (m3/s) is converted to kg/s by multiplying by the
density of water;
hence the input is m3/s of water, not steam. the Engineering Manual and
IO Ref seem to be
confused about this point.
Fred Buhl
JV Dirkes II wrote:
> Perfect! Thanks.
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
> <RRaustad@...> wrote:
>
>> Sorry, I mis-interpreted your pressure comment as being external
>>
> static.
>
>> I will refer you to the Eng Ref, but the mass flow rate of steam is
>> based on 100C steam temperature and assumes saturation (saturated
>> pressure at 100C). The volumetric flow rate calculated from mass flow
>> rate is based on the density of water at 21C (998.2 kg/m3).
>>
>> JV Dirkes II wrote:
>>
>>> Thanks, Richard.
>>>
>>> A minor clarification: Since the energy content of steam at 0 Pa is
>>> different than at some higher pressure, I want to be sure I am using
>>> the same value as E+. Is it correct to assume that E+ reports a cubic
>>> meter of steam at 0 Pa?
>>>
>>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
>>> <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
>>> <RRaustad@> wrote:
>>>
>>>> From the IO Reference document:
>>>>
>>>>
>>>> Group -- Humidifiers
>>>>
>>>>
>>>> Humidifier:Steam:Electrical
>>>>
>>>>
>>>> Field: Rated capacity
>>>>
>>>> The nominal full output water addition rate of the unit in m^3
>>>>
> /sec of
>
>>>> steam.
>>>>
>>>>
>>>> This is the volumetric flow rate of steam at maximum capacity. Since
>>>> humidifiers can add moisture without impacting pressure drop,
>>>>
> pressure
>
>>>> drop is not modeled. There are no immediate plans to connect the
>>>> humidifier to a boiler.
>>>>
>>>> JV Dirkes II wrote:
>>>>
>>>>> Dear E+ Forum,
>>>>>
>>>>> Still hoping to get an answer on this one..... Thanks!
>>>>>
>>>>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
>>>>>
>>> <mailto:EnergyPlus_Support%40yahoogroups.com>
>>>
>>>>> <mailto:EnergyPlus_Support%40yahoogroups.com>, "JV Dirkes II"
>>>>>
>>> <jvd2pe@>
>>>
>>>>> wrote:
>>>>>
>>>>>> Dear E+ Forum,
>>>>>>
>>>>>> A couple questions about humidifiers:
>>>>>> 1) m3/s is (for me) an unusual capacity measure. Is this
>>>>>>
> assumed to
>
>>>>>> be at 0 Pa?
>>>>>> 2) Any plans to create a Humidifier object which uses steam
>>>>>>
> from a
>
>>>>>> boiler? How about natural gas?
>>>>>>
>>>>>> Thank you!
>>>>>>
>>>>>>
>>>>>
>>>> --
>>>> Richard A. Raustad
>>>> Senior Research Engineer
>>>> Florida Solar Energy Center
>>>> University of Central Florida
>>>> 1679 Clearlake Road
>>>> Cocoa, FL 32922-5703
>>>> Phone: (321) 638-1454
>>>> Fax: (321) 638-1439 or 1010
>>>> Visit our web site at: http://www.fsec.ucf.edu
>>>>
> <http://www.fsec.ucf.edu>
>
>>>> UCF - From Promise to Prominence: Celebrating 40 Years
>>>>
>>>>
>>>
>>>
>> --
>> Richard A. Raustad
>> Senior Research Engineer
>> Florida Solar Energy Center
>> University of Central Florida
>> 1679 Clearlake Road
>> Cocoa, FL 32922-5703
>> Phone: (321) 638-1454
>> Fax: (321) 638-1439 or 1010
>> Visit our web site at: http://www.fsec.ucf.edu
>>
>> UCF - From Promise to Prominence: Celebrating 40 Years
>>
>>
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/