Tj is basically right. The outside air system doesn't have any branches 
- you need to
do some thing like this:

  OUTSIDE AIR SYSTEM,
    OA Sys 1,                !- Name
    OA Sys 1 Controllers,    !- Name: Controller List
    OA Sys 1 Equipment,      !- Name of an Air Loop Equipment List
    VAV Sys 1 Avail List;    !- Name of a System Availability Manager List

  CONTROLLER LIST,
    OA Sys 1 Controllers,    !- Name
    CONTROLLER:OUTSIDE AIR,  !- Controller Type 1
    OA Controller 1;         !- Controller Name 1

  AIR LOOP EQUIPMENT LIST,
    OA Sys 1 Equipment,      !- Name
    FAN:SIMPLE:VariableVolume,!- KEY--System Component 1
    Relief Fan 1,             !- Component Name 1
    OUTSIDE AIR MIXER,       !- KEY--System Component 2
    OA Mixing Box 1;         !- Component Name 2

  OUTSIDE AIR MIXER,
    OA Mixing Box 1,         !- Name
    Mixed Air Node 1,        !- Mixed_Air_Node
    OA Mixing Box 1 Inlet Node,  !- Outside_Air_Stream_Node
    OA Mixer Relief Air Outlet Node 1,!- Relief_Air_Stream_Node
    VAV Sys 1 Inlet Node;    !- Return_Air_Stream_Node

  FAN:SIMPLE:VariableVolume,
    Relief Fan 1,            !- Fan Name
    FanAvailSched,           !- Available Schedule
    0.7,                     !- Fan Total Efficiency
    600.0,                   !- Delta Pressure {Pa}
    autosize,                !- Max Flow Rate {m3/s}
    autosize,                !- Min Flow Rate {m3/s}
    0.9,                     !- Motor Efficiency
    1.0,                     !- Motor In Airstream Fraction
    0.35071223,              !- FanCoefficient 1
    0.30850535,              !- FanCoefficient 2
    -0.54137364,             !- FanCoefficient 3
    0.87198823,              !- FanCoefficient 4
    0.000,                   !- FanCoefficient 5
    OA Mixer Relief Air Outlet Node 1,  !- Fan_Inlet_Node
    Relief Air Outlet Node 1;   !- Fan_Outlet_Node
Fred

tjutw wrote:
> You can include a relief fan in the outside air system equipment. The
>  relief fan inlet node is the relief air stream node in the "outside
> air mixer" Object.  
>   
> Given the airflow rate of this relief fan is much less than a return
> fan, you can just decrease the fan pressure from the energy use
> prospective.   
>
> Hope it helps,
>
> Tj Ywh
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@...>
> wrote:
>   
>> Can anyone answer this question?
>>
>> Thanks!
>>
>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@>
>> wrote:
>>     
>>> Dear EPlus Forum,
>>>
>>> I want to model a relief fan working in concert with an air handler. 
>>> This is commonly operated like a variable speed exhaust fan which is
>>> placed in the relief airstream of an outdoor air mixer and removes
>>> excess economizer air. 
>>> As a result the fan heat does not go to the return air stream, and the
>>> airflow rate is often much less than a return fan, since some of the
>>> air exits the building through cracks.
>>> I could not find an example or previous forum discussion which shows
>>> this.  Can anyone give some guidance about how do model this?
>>>
>>> Thanks!
>>>
>>>       
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>   


[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/