Re: [EnergyPlus_Support] AirFlow Window on a Zone
There are two approaches to modeling double facades in EnergyPlus. One
approach uses an airflow window (modeled using WindowGapAirflowControl)
to represent the double façade zone. A second approach models the
double façade zone as a separate zone with glazed exterior and interior
walls. The second approach uses standard window constructions on the
exterior façade that can include a shade/blind on the outside, inside,
or between glazing layers. This exterior window can also be an airflow
window. The interior wall can contain standard window constructions,
but without any shading layer, and cannot be an airflow window. The
Airflow Network model can be used to simulate the effects of airflow
within this exterior double-façade zone and between the outdoors and
adjacent zones whether or not the zone is mechanically conditioned.
Rob
========
Jun Calixihan wrote:
> Dear EnergyPlus support!
>
> I understand from the documentation that the WindowGapAirflowControl
> object
> is associated with a window and not a zone and that the air flows between
> the double/triple glazing. Can this object be associated with a zone,
> perhaps in the future? Is there a way to model a double wall cavity with
> windows (which is a zone) that acts as a plenum with scheduled
> ventilation?
> I uploaded an idf file (bldg1.zip ) from a DesignBuilder model as a sample
> but it has no scheduled cavity ventilation.
>
> Please correct me if I'm wrong on my understanding of
> WindowGapAirflowControl.
>
> Thank you.
>
> rgds,
>
> Jun
>
> [Non-text portions of this message have been removed]
>
>
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/