Re: [EnergyPlus_Support] surface exterior wind speed
The AirflowNetwork model calculates reference wind speed based on weather
wind speed. The equation used in calculations is the second equation in the
Engineering Reference on page 385. The boundary layer height is 60 m. The
field value of Reference height for recorded wind data in the AirflowNetwork
Simulation object is used as "Meteorological station height. If the input of
Wind Pressure Coefficient Type in the AirflowNetwork Simulation object is
"INPUT", the field value of Reference Height for WPC Data in the
AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE COEFFICIENT ARRAY object is used as
the reference height. If the input of Wind Pressure Coefficient Type in the
AirflowNetwork Simulation object is "SURFACE-AVERAGE CALCULATION", the
reference height is 10 m. Then wind pressure is calculated using the first
equation in the section of "Wind pressure calculations" in the Engineering
Reference on page 385. The wind pressure on each surface is applied in
airflow calculations. Please see the last equation on page 380 in the
Engineering Reference.
Lixing
----- Original Message -----
From: "neslihanturkmenoglu" <neslihanturkmenoglu@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Tuesday, May 27, 2008 9:13 AM
Subject: [EnergyPlus_Support] surface exterior wind speed
>I use airflow network object.
>
> I want to learn the steps of;
> 1-zone outdoor wind speed
> and surface exterior wind speed calculation,
> 3-Which speed acts on Airflow Network Volume Flow Rate from Node 2 to
> 1,calculation?
>
> Which fields of objects are used through calculation and how?
> thank you
>
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/