[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Economizer does not function properly
Dear E+ Forum,
The air handler in my current model has an economizer which is staying
at the fixed minimum position at all times on the Winter Design Day.
As a result, the cooling coil operates to create the discharge air
temperature setpoint. I expect that the economizer should increase
the outdoor air flow to accomplish the same result, but it does not.
I've shown the critical objects below and hope someone can direct me
to the problem. Thank you!
p.s., I will upload it, too.
BRANCH,
Branch_AirLoop_AH1, !- Branch Name
Autosize, !- Maximum Branch Flow Rate {m3/s}
OUTSIDE AIR SYSTEM, !- Comp1 Type
OASystem_AH1, !- Comp1 Name
NodeOut_RFan_AH1, !- Comp1 Inlet Node Name
NodeOut_MA_AH1, !- Comp1 Outlet Node Name
PASSIVE, !- Comp1 Branch Control Type
DXSystem:AirLoop, !- Comp2 Type
DXAirLoop_AH1, !- Comp2 Name
NodeOut_MA_AH1, !- Comp2 Inlet Node Name
NodeOut_ClgCoilAir_AH1, !- Comp2 Outlet Node Name
PASSIVE, !- Comp2 Branch Control Type
FAN:SIMPLE:VARIABLEVOLUME, !- Comp3 Type
SFan_AH1, !- Comp3 Name
NodeOut_ClgCoilAir_AH1, !- Comp3 Inlet Node Name
NodeOut_SF_AH1, !- Comp3 Outlet Node Name
ACTIVE, !- Comp3 Branch Control Type
COIL:WATER:SIMPLEHEATING,!- Comp4 Type
HtgCoil_AH1, !- Comp4 Name
NodeOut_SF_AH1, !- Comp4 Inlet Node Name
NodeOut_Air_AH1, !- Comp4 Outlet Node Name
PASSIVE; !- Comp4 Branch Control Type
SET POINT MANAGER:MIXED AIR,
SPMgr_MixedAir_AH1, !- Name
TEMP, !- Control variable:
NodeOut_Air_AH1, !- reference set point node name
NodeOut_ClgCoilAir_AH1, !- fan inlet node name
NodeOut_SF_AH1, !- fan outlet node name
NodeOut_MA_AH1; !- Name of the set point Node or Node List
CONTROLLER:OUTSIDE AIR,
OAController_AH1, !- Name
ECONOMIZER, !- EconomizerChoice
RETURN AIR TEMP LIMIT, !- ReturnAirTempLimit
NO RETURN AIR ENTHALPY LIMIT, !- ReturnAirEnthalpyLimit
NO LOCKOUT, !- Lockout
FIXED MINIMUM, !- MinimumLimit
NodeOut_MA_AH1, !- Control_Node
NodeIn_OA_AH1, !- Actuated_Node
Autosize, !- minimum outside air flow rate {m3/s}
Autosize, !- maximum outside air flow rate {m3/s}
21.1, !- temperature limit {C}
12.8, !- temperature lower limit {C}
, !- enthalpy limit {J/kg}
, !- dew point temperature limit {C}
, !- electronic enthalpy limit curve name
NodeOut_EA_AH1, !- Relief_Air_Outlet_Node
NodeOut_RFan_AH1, !- Return_Air_Node
, !- Minimum Outside Air Schedule Name
, !- Name of VENTILATION:MECHANICAL object
, !- Time of Day Economizer Control
Schedule Name
NO, !- High Humidity Control Flag
ParkingLobbies, !- Humidistat Control Zone Name
1, !- High Humidity Outside Air Flow Ratio
Yes; !- Control High Indoor Humidity based on
Outdoor Humidity Ratio
DXSystem:AirLoop,
DXAirLoop_AH1, !- Name of DX Cooling Coil System
SchCpct_AlwaysOn, !- Availability schedule
NodeOut_MA_AH1, !- DX Cooling Coil System inlet node name
NodeOut_ClgCoilAir_AH1, !- DX Cooling Coil System outlet node name
NodeOut_Air_AH1, !- DX Cooling Coil System Control Node
COIL:DX:COOLINGBypassFactorEmpirical, !- Cooling coil type
ClgCoil_AH1, !- Cooling coil name
None, !- Dehumidification Control Type
Yes, !- Run on Sensible Load
No; !- Run on Latent Load
SET POINT MANAGER:SCHEDULED,
SPMgr_Sched_HC_AH1, !- Name
TEMP, !- Control variable
SchCpct_DischAir_AH1, !- Schedule Name
NodeOut_Air_AH1; !- Name of the set point Node or Node List
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/