[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Staging baseboard and reheat coil



I found the problem! (an incorrectly specified control node)  It's
still not quite working properly, but I'll look at it further on my
own......  Thanks to any who looked at it.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@...>
wrote:
>
> Dear E+ Forum,
> 
> In further attempts to solve this problem, I removed the baseboard
> completely .... and found that the reheat coils still do not operate.
>  The file now is very similar to the example file 5ZoneCostEst.idf.
> 
> I suspect that my problem in this file is the same as exists in the
> baseboard file, but I still need help finding the problem.  Thanks in
> advance. (File uploaded shortly)
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@>
> wrote:
> >
> > Dear E+ Forum,
> > 
> > I'm finally evaluating output for the model which I want the baseboard
> > to act as the first stage of heating (reheat coil is the 2nd stage). 
> > The baseboard is operating, the reheat coil is not operating (zero
> > flow), and the room is not reaching the setpoint temperature in the
> > heating season.
> > 
> > I'm using objects as shown below.  May I have suggestions regarding
> > what's incorrect, please?
> > 
> > ZONE EQUIPMENT LIST,
> >     ZoneEqList_Floors 3thru5,!- Name
> >     BASEBOARD HEATER:WATER:CONVECTIVE,  !- KEY--Zone Equipment Type 1
> >     BasebdWtr_Floors 3thru5, !- Type Name 1
> >     1,                       !- Cooling Priority 1
> >     1,                       !- Heating Priority 1
> >     AIR DISTRIBUTION UNIT,   !- KEY--Zone Equipment Type 2
> >     AirDistUnit_Floors 3thru5,  !- Type Name 2
> >     2,                       !- Cooling Priority 2
> >     2,                       !- Heating Priority 2
> >     ZONE EXHAUST FAN,        !- KEY--Zone Equipment Type 3
> >     ZoneEF_Floors 3thru5,    !- Type Name 3
> >     3,                       !- Cooling Priority 3
> >     3;                       !- Heating Priority 3
> > 
> > AIR DISTRIBUTION UNIT,
> >     AirDistUnit_Floors 3thru5,  !- Air Distribution Unit Name
> >     NodeIn_Zn_Floors 3thru5, !- Air Dist Unit Outlet Node Name
> >     SINGLE DUCT:VAV:REHEAT,  !- KEY--System Component Type 1
> >     RhtCTRL_Floors 3thru5;   !- Component Name 1
> > 
> > SINGLE DUCT:VAV:REHEAT,
> >     RhtCTRL_Floors 3thru5,   !- Name of System
> >     SchCpct_AlwaysOn,        !- System Availability schedule
> >     NodeOut_VVDpr_Floors 3thru5,  !- DAMPER Air Outlet Node
> >     NodeOut_ZnSpltr_Floors 3thru5,  !- UNIT Air Inlet Node
> >     Autosize,                !- Maximum air flow rate {m3/s}
> >     0.3,                     !- Zone Minimum Air Flow Fraction
> >     NodeIn_RhtWtr_ParkingLobbies,  !- Control node
> >     COIL:WATER:SIMPLEHEATING,!- Reheat Component Object
> >     RhtCoil_Floors 3thru5,   !- Name of Reheat Component
> >     Autosize,                !- Max Reheat Water Flow {m3/s}
> >     0,                       !- Min Reheat Water Flow {m3/s}
> >     NodeIn_Zn_Floors 3thru5, !- UNIT Air Outlet Node
> >     0.001,                   !- Convergence Tolerance
> >     NORMAL;                  !- Damper Heating Action
> > 
> > COIL:Water:SimpleHeating,
> >     RhtCoil_Floors 3thru5,   !- Coil Name
> >     SchCpct_HtgAvail_AH1,    !- Available Schedule
> >     Autosize,                !- UA of the Coil {W/K}
> >     Autosize,                !- Max Water Flow Rate of Coil {m3/s}
> >     NodeIn_RhtWtr_Floors 3thru5,  !- Coil_Water_Inlet_Node
> >     NodeOut_RhtWtr_Floors 3thru5,  !- Coil_Water_Outlet_Node
> >     NodeOut_VVDpr_Floors 3thru5,  !- Coil_Air_Inlet_Node
> >     NodeIn_Zn_Floors 3thru5, !- Coil_Air_Outlet_Node
> >     UA and Design Water Flow Rate,  !- Coil Performance Input Method
> >     Autosize,                !- Nominal Capacity {W}
> >     82.2,                    !- Design Inlet Water Temperature {C}
> >     12.8,                    !- Design Inlet Air Temperature {C}
> >     65.6,                    !- Design Outlet Water Temperature {C}
> >     40.6;                    !- Design Outlet Air Temperature {C}
> > 
> > 
> > 
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@>
> > wrote:
> > >
> > > Thanks, Matthew!  I remember now about that prioritization
within Zone
> > > Equipment List; we'll see how it works for this situation.
> > > 
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Matthew Flannery"
> > > <matthew.flannery@> wrote:
> > > >
> > > > Have you tried looking at your zone equipment list?  This only
> > works if
> > > > you're out of compact mode.  In this tab you define your zone
> heating
> > > > priority for reheat coils and baseboard heaters.
> > > > 
> > > >  
> > > > 
> > > >  
> > > > 
> > > > !-   ===========  ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST
> > ===========
> > > > 
> > > >  
> > > > 
> > > > ZONE EQUIPMENT LIST,
> > > > 
> > > >     Zone_1 Equipment,        !- Name
> > > > 
> > > >     AIR DISTRIBUTION UNIT,   !- KEY--Zone Equipment Type 1
> > > > 
> > > >     Zone_1 Reheat Coil,      !- Type Name 1
> > > > 
> > > >     2,                       !- Cooling Priority 1
> > > > 
> > > >     2,                       !- Heating Priority 1
> > > > 
> > > >     BASEBOARD HEATER:WATER:CONVECTIVE,  !- KEY--Zone Equipment
> Type 2
> > > > 
> > > >     Zone_1 Baseboard,        !- Type Name 2
> > > > 
> > > >     1,                       !- Cooling Priority 2
> > > > 
> > > >     1;                       !- Heating Priority 2
> > > > 
> > > >  
> > > > 
> > > >  
> > > > 
> > > > Matthew Flannery, LEED A.P.
> > > > 
> > > > Mechanical Engineer
> > > > 
> > > > Buro Happold Consulting Engineers, PC
> > > > 100 Broadway 
> > > > New York, NY 10005
> > > > USA
> > > > 
> > > >  
> > > > 
> > > >  
> > > > 
> > > >  
> > > > 
> > > > ________________________________
> > > > 
> > > > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > > > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of JV
> Dirkes II
> > > > Sent: Sunday, April 27, 2008 8:02 PM
> > > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > > > Subject: [EnergyPlus_Support] Staging baseboard and reheat coil
> > > > 
> > > >  
> > > > 
> > > > Dear E+ Forum,
> > > > 
> > > > I'm trying to figure out how to make baseboard heating and a
reheat
> > > > coil act as Stage 1 and Stage 2 of the zone's heating. Stage 2
(the
> > > > reheat coil) should stay off until the Baseboard (Stage 1) is at
> full
> > > > capacity.
> > > > 
> > > > Thanks in advance.
> > > > 
> > > >  
> > > > 
> > > > 
> > > > 
> > > > This message has been scanned by MailController -
> > > www.MailController.altohiway.com
> > > > 
> > > > 
> > > > [Non-text portions of this message have been removed]
> > > >
> > >
> >
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/