[EnergyPlus_Support] Re: Enthalpy conversion from US --> SI
Dear Phillip,
This is exactly the type of feedback I was hoping for! I'm hoping
that you can take me one step further as well.
I searched the E+ documentation for info on the PsyHFnTdbW function,
and found that it is actually a function of both dry bulb temp and
humidity ratio, which is consistent with my calculations in US
measure, shown below.
Function Enth(DB, W)
' Calculate Enthalpy given dry bulb temp, humidity ratio
Enth = Cp(DB) * DB + W * (1061 + 0.444 * DB)
I did not find the actual function equation, however. If I understand
you correctly, I could perform a straight US --> SI conversion for DB
and W, and then correct for the different zero values. Can you tell
me the expected SI / E+ units for W? Cp?
Thanks!
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Philip Haves <phaves@...>
wrote:
>
> The conversion is not a straight multiplication because the zero of the
> IP enthalpy scale is dry air at 0 degrees Fahrenheit whereas the
zero of
> the SI enthalpy scale is dry air at 0 degrees Celsius.
>
> Using the values of the coefficients in Function PsyHFnTdbW in
> Energyplus and the corresponding IP values obtained using the
conversion
> factors in Chapter 37 of the ASHRAE Handbook of Fundamentals:
>
> Hip = 0.2398*((1.8*Hsi/1.00484E3)+32) Btu/lb
>
> Hsi =1.00484E3*(((Hip/0.2398) -32)/1.8) J/kg
>
>
>
> On 5/28/2008 1:31 PM, JV Dirkes II wrote:
> >
> > Dear E+ Forum,
> >
> > Will someone please confirm the following? (I'm not familiar with
> > enthalpy values in SI measure and want to be sure I am converting
> > values properly) Thanks!
> >
> > Enthalpy (US) = BTU/lb
> > Enthalpy (SI / E+) = J/kg
> >
> > "X" BTU/lb * 1055 J/BTU * 2.2 lb/kg = "X" * 2321 J/kg
> >
> > e.g., 28 BTU/lb = 64,988 J/kg
> >
> >
>
> --
> __________________________________
> Philip Haves
> Leader, Commercial Building Systems Group
> Lawrence Berkeley National Laboratory
> One Cyclotron Road, MS 90R3111
> Berkeley, CA 94720-8134
> (510) 486 6512 (office)
> (510) 486 4089 (fax)
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/