[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Warning: "Air volume flow rate per watt ... is out of range .."
File will be uploaded shortly. Thanks!
p.s., V2.2.026 cause the error.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> That particular error is not supposed to occur in a simulation (it's
> mainly used by the model developer). You have somehow managed to trip
> this error. Please upload the file that causes this error.
>
> Two-speed compressors use speed ratio and cycling ratio to define the
> performance. The speed ratio determines the staging. If the first stage
> compressor can not meet the load, the second stage compressor turns on.
> If the load is lower than the full speed compressor capacity (for first
> or second stage), the compressor will cycle. The cycling ratio is the
> fraction of time the compressor is on for a given time step.
>
> JV Dirkes II wrote:
> >
> > Late-breaking developments....
> >
> > When using the Coil:DX:Multispeed:CoolingEmpirical with curves from
> > the example file, I get a fatal error,
> >
> > " ** Fatal ** DX unit cycling ratio calculation failed: cycling
> > limits exceeded, for unit=DXAIRLOOP_AH1"
> >
> > Apparently I not only need to create a curve, but it has to comply
> > with some sort of test. What is the "cycling ratio calculation"? I
> > could not find a discussion of that in the reference docs, other than
> > when it's used for chillers. Chillers seem to allow any part load
> > ratio at all, defaulting to the minimum specified PLR when the
> > calculation of PLR falls below the minimum. DX must not work that
way....
> >
> > Thanks again.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "JV Dirkes II"
<jvd2pe@>
> > wrote:
> > >
> > > Thanks, Richard.
> > >
> > > This looks very promising, since this object is intended for VAV
> > > systems and the COIL:DX:COOLINGBypassFactorEmpirical object is
> > > intended (I now see) for single zone DX systems.
> > >
> > > After reading the IO Reference and looking at some manufacturer
> > > literature, a couple things are apparent:
> > > 1) The example file indicates that its curves are applicable to a
> > > small system, which I guess to be smaller than 15 US
refrigeration tons
> > > 2) it looks like a somewhat daunting task to create these curves for
> > > larger systems from manufacturer literature, since I have no
> > > experience at creating biquadratic curve fits.
> > >
> > > That said, is anyone in the forum
> > > a) aware of references which have information on this topic for
> > > systems larger than 20 tons? (with multiple compressors in
> > > combinations up to, say, 200 tons)
> > > b) familiar with easy to use, inexpensive curve-fitting software
that
> > > would be applicable for this purpose?
> > > c) aware of a refrigeration manufacturer who has curves already
> > > prepared for their equipment?
> > >
> > > Thank you!
> > >
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "Richard Raustad"
> > > <RRaustad@> wrote:
> > > >
> > > > I sent an earlier email, but I don't see it. Here is a brief
summary
> > > > of the previous email.
> > > >
> > > > Use the 2-speed DX coil model
Coil:DX:Multispeed:CoolingEmpirical to
> > > > estimate the performance. First stage is about 1/3 capacity
with an
> > > > EIR curve set to 1 (or close to that). Second stage is full
capacity
> > > > with DX cooling coil EIR curves that replicate an unloading
> > > > compression system. If you don't have the data, use the typical DX
> > > > cooling coil EIR curves. Check with manufacturers for performance
> > > > data to more closely model the energy input for unloading
compressors
> > > > at part load.
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "JV Dirkes II"
> > > > <jvd2pe@> wrote:
> > > > >
> > > > > Dear Richard,
> > > > >
> > > > > I believe that there's a valid reason for the warning and
I'm glad
> > > > > it's part of E+. My goal is to find out how to tell E+ that
"It's
> > > > OK"
> > > > > because there is hot gas bypass control on the DX system or some
> > > > other
> > > > > unloading control which allows operation at very low part loads?
> > > > >
> > > > > Better yet, how do I tell E+ to model the performance of such a
> > > > control?
> > > > >
> > > > >
> > > > >
> > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > > > <RRaustad@> wrote:
> > > > > >
> > > > > > Change your report variables to "detailed" to see the
values at
> > > > each
> > > > > > simulation time step. The HVAC system time steps are
allowed to
> > > > reduce
> > > > > > down to 1-minute. This message is typical of VAV systems where
> > > > the air
> > > > > > flow is reduced far lower than should be allowed for DX
systems.
> > > > VAV
> > > > > > chilled water systems do not have this restriction. You can
> > > > report out
> > > > > > the DXSystem Part-Load Ratio to back calculate the coil outlet
> > > > air
> > > > > > temperature to see if the coil is near freezing.
> > > > > >
> > > > > > System Convergence Limits,
> > > > > > 1, !- Minimum System Time Step {minutes}
> > > > > > 80; !- Maximum HVAC Iterations
> > > > > >
> > > > > > Report Variable,
> > > > > > NodeOut_MA_AH1, !- Key_Value
> > > > > > System Node VolFlowRate, !- Variable_Name
> > > > > > detailed; !- Reporting_Frequency
> > > > > >
> > > > > > Report Variable,
> > > > > > *, !- Key_Value
> > > > > > DXSystem Part-Load Ratio, !- Variable_Name
> > > > > > detailed; !- Reporting_Frequency
> > > > > >
> > > > > > Using data in the csv output file at 07/15 00:11:00:
> > > > > > Tout,avg = Tcoil,out(PLR)+Tcoil,in(1-PLR)
> > > > > > Tcoil,out = (Tout,avg-Tcoil,in(1-PLR))/PLR
> > > > > > Tcoil,out = (12.20674-20.776(1-0.348526))/0.348526
> > > > > > Tcoil,out = -3.811 C
> > > > > >
> > > > > > Tout,avg = NODEOUT_CLGCOILAIR_AH1:System Node Temp[C]
> > > > > > Tcoil,in = NODEOUT_MA_AH1:System Node Temp[C]
> > > > > > PLR = DXAIRLOOP_AH1:DXSystem Part-Load Ratio
> > > > > >
> > > > > > The warnings are trying to convey that there is a good
chance of
> > > > coil
> > > > > > frosting and compressor failure.
> > > > > >
> > > > > > JV Dirkes II wrote:
> > > > > > >
> > > > > > > Dear E+ Forum,
> > > > > > >
> > > > > > > After spending considerably more time trying to resolve this
> > > > problem,
> > > > > > > I'm now seeing 6700 warnings after cleaning up a few minor
> > > > > > > discrepancies. I'm hoping that someone can take a look
at the
> > > > file I
> > > > > > > uploaded to determine the cause!
> > > > > > >
> > > > > > > p.s., The uploaded file is called "AirFlowperWatt.zip"
> > > > > > >
> > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, "JV
Dirkes II"
> > > > > <jvd2pe@>
> > > > > > > wrote:
> > > > > > > >
> > > > > > > > Dear E+ Forum,
> > > > > > > >
> > > > > > > > I am looking at this warning again, trying to understand
> > > > it... and
> > > > > > > > failing to do so.
> > > > > > > >
> > > > > > > > In short:
> > > > > > > > The warning occurs over 3700 times in 3 Design days; this
> > > > seems
> > > > > > > excessive!
> > > > > > > > The warning appears to occur multiple times in a
single minute
> > > > > (I get
> > > > > > > > multiple warning messages for the exact same time,
coil and
> > > > design
> > > > > > > > day. I have specified 4 timesteps per hour, but the
warnings
> > > > > refer to
> > > > > > > > minutes that are NOT timesteps.)
> > > > > > > > The "air volume per watt" is an acceptable value at the
> > > > timestep (It
> > > > > > > > is within the acceptable range noted in the warning.)
> > > > > > > >
> > > > > > > > Since this warning occurs for a non-timestep minute,
> > > > something seems
> > > > > > > > to be going on in the background. In addition, there
are no
> > > > other
> > > > > > > > errors or warnings which suggest a cause for this one.
> > > > > > > >
> > > > > > > > Thanks in advance.
> > > > > > > >
> > > > > > > >
> > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Don Shirey
> > > > > <shirey@> wrote:
> > > > > > > > >
> > > > > > > > > The warning can be an indication of very low supply air
> > > > flow rate
> > > > > > > > > compared to the coil's cooling capacity.... and very low
> > > > > outdoor air
> > > > > > > > > temperatures may also be contributing.
> > > > > > > > >
> > > > > > > > > Find the autosized air flow rate and cooling coil
capacity
> > > > in the
> > > > > > > .eio
> > > > > > > > > file ... and then look at the
> > > > COIL:DX:COOLINGBypassFactorEmpirical
> > > > > > > > > documentation in the IO Reference and Engineering
Reference
> > > > > for how
> > > > > > > > that
> > > > > > > > > coil model works and how the flow rate/capacity
values are
> > > > used.
> > > > > > > > >
> > > > > > > > >
> > > > > > > > > JV Dirkes II wrote:
> > > > > > > > > > Dear E+ Forum,
> > > > > > > > > >
> > > > > > > > > > The Air handler for a current E+ model (v2.2) has a
> > > > > > > > > > COIL:DX:COOLINGBypassFactorEmpirical cooling coil
and a
> > > > hot
> > > > > water
> > > > > > > > > > heating coil. The model runs, but has hundreds of
> > > > instances
> > > > > of this
> > > > > > > > > > warning or "Full load outlet temperature indicates a
> > > > > possibility of
> > > > > > > > > > frost/freeze...", which appears to have a similar
cause.
> > > > All
> > > > > > > > > > capacities are autosized and I am simulating only 3
> > > > Design Days
> > > > > > > with 4
> > > > > > > > > > timesteps per hour (so the hundreds of warnings
seem to
> > > > be too
> > > > > > > many!)
> > > > > > > > > >
> > > > > > > > > > Will someone help me understand the cause of the
error and
> > > > > how to
> > > > > > > > > > resolve it? Thank you!
> > > > > > > > > >
> > > > > > > > > >
> > > > > > > > > > ------------------------------------
> > > > > > > > > >
> > > > > > > > > > The primary EnergyPlus web site is found at:
> > > > > > > > > > http://www.energyplus.gov <http://www.energyplus.gov>
> > <http://www.energyplus.gov <http://www.energyplus.gov>>
> > > > > > > > > >
> > > > > > > > > > The group web site is:
> > > > > > > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > <http://groups.yahoo.com/group/EnergyPlus_Support/>
> > > > > > > <http://groups.yahoo.com/group/EnergyPlus_Support/
> > <http://groups.yahoo.com/group/EnergyPlus_Support/>>
> > > > > > > > > >
> > > > > > > > > > Attachments are not allowed -- please post any
files to
> > > > the
> > > > > > > > appropriate folder in the Files area of the Support
Web Site.
> > > > > > > > > >
> > > > > > > > > > EnergyPlus Documentation is searchable. Open
> > > > EPlusMainMenu.pdf
> > > > > > > > under the Documentation link and press the "search"
button.
> > > > > > > > > > Yahoo! Groups Links
> > > > > > > > > >
> > > > > > > > > >
> > > > > > > > > >
> > > > > > > > >
> > > > > > > >
> > > > > > >
> > > > > > >
> > > > > >
> > > > > > --
> > > > > > Richard A. Raustad
> > > > > > Senior Research Engineer
> > > > > > Florida Solar Energy Center
> > > > > > University of Central Florida
> > > > > > 1679 Clearlake Road
> > > > > > Cocoa, FL 32922-5703
> > > > > > Phone: (321) 638-1454
> > > > > > Fax: (321) 638-1439 or 1010
> > > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > > > > >
> > > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > > >
> > > > >
> > > >
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/