Re: [EnergyPlus_Support] Re: Sizing Parameters object has no influence



I'm glad it works!

Likewise, you can just enter one Zone Sizing object -- if you want 
that to apply to all the zones (I believe).

Or enter one and specific ones that you want to be specfic about.

Linda

At 03:13 PM 6/5/2008, JV Dirkes II wrote:

>Thanks, Linda.
>
>You got me thinking.  Apparently the trick is to leave the Zone Sizing
>"sizing factor" BLANK.  I tried that and it now works!
>
>--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> wrote:
> >
> > According to the IORef:
> >
> > Sizing Parameters,
> > Field: sizing factor
> > The global sizing ratio applied to all of the zone design load and
> > air flow rates.
> >
> > Zone Sizing,
> > Field: Zone sizing factor
> > This input is a zone level sizing ratio. The zone design heating and
> > cooling air flow rates and
> > loads will be multiplied by the number input in this field. This
> > input overrides the building level
> > sizing factor input in the Sizing Parameters object.
> >
> > So, since you supplied a Zone Sizing factor, it overrode the Sizing
> > parameters factor.
> >
> > I think if you left that blank in the Zone Sizing object, it would
> > take the global one but it may not be quite that simple.
> >
> > Not my area of expertise.
> >
> > Linda
> >
> > At 02:52 PM 6/5/2008, JV Dirkes II wrote:
> >
> > >Dear E+ Forum,
> > >
> > >Results of a test are shown below, in which it seems that the Sizing
> > >Parameters object has no influence at all.  The Zone Sizing object,
> > >however, works as expected.  What might cause the Sizing Parameters
> > >object to not function?
> > >
> > >                 Test 1  Test 2  Test 3
> > >                 Load (W)        Load (W)        Load
> > > (W)
> > >Zone #1 Cooling 13,288  13,288  15,281
> > >Zone #1 Heating 29,510  29,510  33,937
> > >Zone #2 Cooling 848     848     975
> > >Zone #2 Heating 5,549   5,549   6,382
> > >Zone #3 Cooling 140,762 140,762 161,876
> > >Zone #3 Heating 413,764 413,764 475,829
> > >
> > >         Remarks Test 1:  No Sizing Parameters object, Zone Sizing
> > > set at 1.0
> > >                 Test 2:  Sizing Parameters object set for 1.15,
> > > Zone Sizing set at
> > >1.0 (No change!)
> > >                 Test 3:  Sizing Parameters object set for 1.0, Zone
> > > Sizing set at
> > >1.15 (Expected change)
> > >
> > >
> > >
> > >------------------------------------
> > >
> > >The primary EnergyPlus web site is found at:
> > >http://www.energyplus.gov
> > >
> > >The group web site is:
> > >http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > >Attachments are not allowed -- please post any files to the
> > >appropriate folder in the Files area of the Support Web Site.
> > >
> > >EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf
> > >under the Documentation link and press the "search" button.
> > >Yahoo! Groups Links
> > >
> > >
> > >
> >
> > [Non-text portions of this message have been removed]
> >
>
>
>
>------------------------------------
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the 
>appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
>under the Documentation link and press the "search" button.
>Yahoo! Groups Links
>
>
>

[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/