Re: [EnergyPlus_Support] Help on a detached shading issue!
If you want them not to influence the heat
transfer solution, you must enter the blocks as
detached shading not as HeatTransfer surfaces (==
not sure if your interface of "adiabatic" is doing this for you or not).
The warning just tells you what outside
conditions will end up being used for these surfaces.
I will try to look at your uploaded file.
Linda
At 09:41 AM 6/9/2008, Nuno Costa Brandão wrote:
>Dear All,
>
>I´m simulating a multi-story building from which I choose one floor to
>model. Around the building there are other buildings which block solar
>radiation so I choose to model them as single zone blocks, defining
>all of its surfaces as adiabatic so they do not enter in heat transfer
>calculations. However, as they were drawn after the floor model, they
>have negative coordinates which results in an error issue, and also
>little influence in the final results(PURCHASED AIR HEATING AND
>COOLING RATES):
>
>ERROR MESSAGE:
> ** Warning ** CalcSurfaceCentroid: 209 Surfaces have the Z
>coordinate < 0.
> ** ~~~ ** ...in any calculations, Wind Speed will be 0.0 for
>these surfaces.
> ** ~~~ ** ...in any calculations, Outside temperatures will be
>the outside temperature + 9.750E-003 for these surfaces.
> ** ~~~ ** ...that is, these surfaces will have conditions as
>though at ground level.
>
>I must guarantee the sun blockage correctly, is this procedure
>appropriated?
>I´m uploading the file so that you can have a look at it.
>
>Thanks for the help
>Nuno
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/