[EnergyPlus_Support] Re: Fan Electric Power



Thank you, for everything.
Ana.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" 
<jvd2pe@...> wrote:
>
> Dear Ana,
> 
> Communicating only in text makes things more difficult!  I'll try 
again
> (still using US units of measure)!
> 
> Using this example:
>                                            
FAN:SIMPLE:VARIABLEVOLUME,
> Fan Name                      RFan_AH1,
> Available Schedule   SchCpct_FanOpern,
> Fan Total Efficiency    0.485,
> Delta Pressure               995,  (4" w.c.)
> Max Flow Rate              13.1372, (27,836 CFM)
> Min Flow Rate    0,
> Motor Efficiency    .91,
> Motor In Airstream Fraction    1,
> FanCoefficient 1    .0013,
> FanCoefficient 2    .147,
> FanCoefficient 3    .9506,
> FanCoefficient 4    -.0998,
> FanCoefficient 5    0,
> Fan_Inlet_Node    NodeOut_EA_AH1,
> Fan_Outlet_Node    NodeOut_EFan_AH1;
> End-Use Subcategory
> 
> Notes:
> 
>     * Max Flow Rate is selected from equipment data (as shown 
above) or
> determined from the .eio file when autosizing.  As mentioned 
previously,
> remember to include the effect of any sizing parameter.  Also, for 
a VAV
> fan, make sure that it's actually operating at peak flow or the
> coefficients will be active and reduce power consumption.
> 
>     * Delta pressure is selected from equipment data
>     * Fan Total Efficiency is taken from equipment data (Note that 
the IO
> Reference defines this as INCLUDING the motor efficiency)
> For this fan, I expect power to be:
> 
> Brake HP = CFM * DeltaP / TotalEff'y / 6,356
> 
> W                = CFM * DeltaP / TotalEff'y / 6,356 * 746
> 
>                      = 27,836 * 4 / .485 / 6,356 * 746
> 
>                      = 26,945
> 
> When I run this fan object in an E+ model, the .csv file reports 
26,761W
> at the time when Flow Rate = Max Flow Rate.  That's pretty close
> agreement!
> 
> I hope this helps.
> 
> p.s., I applaud your error checking efforts.  With hundreds or 
thousands
> of inputs, it is very important to make sure the output makes sense!
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "anarui.oliveira"
> <anarui.oliveira@> wrote:
> >
> > Sorry, could you add some legends to make sure I'm looking at the
> > right variables?...
> > If I understood, those calculations correspond to an independent
> > estimate of electric power consumption of the fans?
> >
> > In the cases when I detected large differences between E+ and
> > supplier data, the supplier data indicated straightforward 
electric
> > power consumption of the fans... and delta-Pressure and nominal
> > airflow. I used that dP and airflow (which does not vary
> > significantly beacuse I was using CAV models) to feed to E+ and
> > obtain its electric power estimate... I had also high values of
> > (total) efficiency (above 0.7), but even trying to reduce those 
in E+
> > did not increase the power estimate to values anywhere near the
> > supplier data...
> >
> > I guess the supplier data may sometimes include the effect of the
> > selected fans not working at nominal conditions for the intended
> > aiflows, but still... differences of twice over?...
> >
> > Anyway, thanks for everything,
> > Ana.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II"
> > jvd2pe@ wrote:
> > >
> > > Dear Ana,
> > >
> > > I get excellent agreement for fan power when using (US
> > measurements):
> > >
> > > BHP =    CFM x    Î"P
> > >                    η x    6,355
> > >
> > > =   f3 x    in. w.c. x    62.316 lb              x     min-HP
> > >      min               η            ft2 x 12 in. w.c.     
> 33,000
> > > ft-lb
> > >
> > > =    CFM x     Î"P
> > >            η  x   6,355
> > >
> > > It is important to know the mechanical efficiency of the 
fan "η"
> > > from a fan chart, or to derive it from known Brake HP.
> > >
> > > Also, you must make sure that the E+ report reflects the correct
> > flow. A
> > > relief fan, for example, may never operate at the rated airflow 
and
> > the
> > > .eio report only shows Watts for the modeled airflow.  The .ssz 
will
> > > show the design airflow.
> > > If you are using a sizing factor greater than 1.0, don't forget 
to
> > use
> > > the rated airflow x sizing factor as your basis for power
> > calculations.
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "anarui.oliveira"
> > > <anarui.oliveira@> wrote:
> > > >
> > > > Hi, me again.
> > > >
> > > > Has anyone tried to compare the E+ estimates of Fan Electric 
Power
> > > with
> > > > rated electric consumptions for these equipments?
> > > > I've been trying to "calibrate" these values, but I keep 
getting
> > E+
> > > > plus estimates much lower than supplier data (like 2 to 10 
times
> > > > smaller values, for E+ estimate of Fan electric power).
> > > >
> > > > Regards,
> > > > Ana Rui.
> > > >
> > >
> >
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/