Re: [EnergyPlus_Support] Turning system on/off based on temperature predictions



This is certainly possible in E+. There are several ways to do this in 
E+. The control type schedule in the thermostat object could be used to 
switch between uncontrolled and cooling/heating, or the temperature set 
point schedule could be set to 0 and 99 as necessary to turn the unit on 
and off. The availability schedule could also be used in this same 
fashion by setting the schedule to 0 when you want the unit off and 
non-zero values when you want the unit on.  The AC system could turn 
full on or run at part-load depending on which method you decide to use.

nick_gski wrote:
>
> I would like to tell a system, e.g. a heat pump, to turn on/off
> arbitrarily for each hour, not based on current zone or node
> temperatures but based on my own algorithms that dictate an optimal
> control sequence. Is this doable in energyplus? Could I create a
> dummy zone that controls the systems? Can I create an on/off schedule
> for the equipment itself, rather than an availability schedule or a
> setpoint schedule?
>
> The best thing I can think of is to tweak the availability and
> setpoint schedules to force the system into 100% on or off when I want
> it so.
>
> Thanks,
> Nick
>
> ---
> Nick Gayeski
> Mitsubishi Electric Research Lab
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/