[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] airflow between-core perimeter zones
Hi all,
I am modelling a one-story Hangar which is a large single room. I want
to split this room into 4 perimeter (N,S,E,W) and one core zone,
however since this is a single room (no internal partitions in the
actual case) there needs to be air exchange between the zones.
My question is:
Using cross-mixing, is it the only way to simulate this configuration?
(and what ach would be a good guess, in terms of air exchange between
to adjacent zones?)
Is there any "hole" command (as in Design builder) in Energy+ to
achieve air exchange between the zones? (or can I just remove the
internal partitions after defining the zones separately?)
Thanks in advance for all your help!
Alper
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/