Dear Alper,

In my opinion, a very large hangar (i.e., multiple A320s) will
probably exhibit distinct zone characteristics, but small to mid-size
hangars will not.  In addition, the HVAC system will probably be
designed to favor comfort in the occupied area, which is often the
floor only; no one works near the walls or ceiling.

Finally, hangar door opening will completely destroy comfort and
setpoint control while open, making "zones" meaningless.

For these reasons, I recommend that you consider using a single zone
instead of multiple zones.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "alpererten"
<alpererten@...> wrote:
>
> Hi all,
> 
> I am modelling a one-story Hangar which is a large single room. I want 
> to split this room into 4 perimeter (N,S,E,W) and one core zone, 
> however since this is a single room (no internal partitions in the 
> actual case) there needs to be air exchange between the zones.
> 
> My question is:
> 
>  Using cross-mixing, is it the only way to simulate this configuration? 
> (and what ach would be a good guess, in terms of air exchange between 
> to adjacent zones?)
> 
>  Is there any "hole" command (as in Design builder) in Energy+ to 
> achieve air exchange between the zones? (or can I just remove the 
> internal partitions after defining the zones separately?)
> 
> Thanks in advance for all your help!
> Alper
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/