[EnergyPlus_Support] Re: Reformulated Electric EIR chiller



The leaving chilled water temperature is 6 degree C and the leaving 
condenser water is 35 degree C. 

thanks. 

Yiqun

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>
> Yiqun:
> 
> When a normal chiller is used, leaving chilled water temperature 
and 
> entering cooling water temperature are used to calculate COP using 
the 
> Energy Input to Cooling Output Ratio Function of Temperature Curve 
and Part 
> Load Ratio curve. When a reformulated chiller is selected, Leaving 
Chilled 
> Water Temperature and Leaving Condenser Water Temperature are used 
to 
> calculate an EIR modifier, instead of entering cooling water 
temperature. 
> Leaving Condenser Water Temperature and Part Load Ratio are used to 
> calculate part load penalty. Could you let me know what leaving 
condenser 
> water temperature and leaving chilled water temperature are?
> 
> Thanks.
> 
> Lixing
> ----- Original Message ----- 
> From: "&#28504;&#27589;&#32676;" <yiqunpan@...>
> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> Sent: Thursday, July 17, 2008 3:52 AM
> Subject: [EnergyPlus_Support] Reformulated Electric EIR chiller
> 
> 
> > On the Engineering Reference, it is said that the reformulated EIR
> > chiller model can improve the accuracy of simulating a VSD chiller
> > significantly from normal EIR chiller model. However I got some
> > ubnormal results from the reformulated model. I selected a model 
from
> > the chiller datasets of E+ - ReformEIRChiller Trane CVHF
> > 2317kw/6.33COP/VSD, and tried to obtain the changing trend of COP
> > following its part load ratio and found that its COP decreases 
with the
> > part load ratio decreases, with the same leaving chilled water
> > temperature and entering cooling water temperature. I also tried 
with a
> > normal EIR chiller model from the datasets, but got different 
changing
> > trend, which COP reaches its peak when the part load ratio is 
aroung
> > 50%. It seems that the result from normal EIR chiller model is 
more
> > close to the actural condition.
> >
> > Has anybody tried the same thing and is able to tell me something 
about
> > it? thanks.
> >
> > Yiqun Pan
> > Tongji University
> >
> >
> > ------------------------------------
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the 
appropriate 
> > folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
under the 
> > Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/