Re: [EnergyPlus_Support] EXAMPLE FILE HELP - "BenchmarkLargeHotelNew_USA_IL_CHICAGO-OHARE.idf"



In this file, there are 4 set point managers used for the air primary 
loop. The scheduled set point managers (there are actually 2 but only 1 
is really needed since they both use the same schedule - the 2nd one 
does not hurt anything) place a temperature set point at the outlet of 
the air primary loop. Then there are 2 mixed air set point managers that 
use the air primary loop outlet node temperature set point as the 
reference node temperature, adjust for fan heat, and place a calculated 
temperature set point at the outlet of both the heating and the cooling 
coil (again 1 mixed air set point manager could have been used here, 
with a node list specifying the cooling and heating coil outlet nodes). 
So the result is that both the cooling coil and heating coil have their 
own temperature set point at their individual outlet nodes.

Nuno Costa Brandão wrote:
>
> Dear All,
>
> I´m studying the "BenchmarkLargeHotel" example file. I have a small
> dough that I would like to clarify and I was hoping to get some
> guidance help.
>
> Referring to the Air Primary Loop coil controls, why does the cooling
> coil control, is referred to the air loop outlet node "VAV WITH REHEAT
> Supply Equipment Outlet Node" and not "VAV WITH REHEAT_CoolC-VAV WITH
> REHEAT_HeatCNode", which is the outlet node from the air leaving the
> cooling coil on the air loop? The control node for the heating coil is
> referred to the outlet air node "VAV WITH REHEAT_HeatC-VAV WITH REHEAT
> FanNode" leaving the coil and the last one from the air loop.
>
> I would be greatfull for some guidance help.
> Nuno
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/