Hi Richard,
Following the last post, so since both the heating coil and cooling
coil have their one temperature setpoints defined at their individual
outlet nodes, it´s indifferent whether the "control node" for the
cooling coil is referred to the outlet air node, or the outlet air
loop node?
In other example files ("5zoneWaterSystems.idf")with similar loop
structure, both controllers have their control node referred to the
outlet air loop node, can I assume this procedure as a "thumb rule"
procedure? i.e. Always refer the cooling and heating coils control
nodes to the "air loop outlet node"?
Thank you very much for your help
Nuno
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/