1) It is perfectly acceptable to combine rooms into a single zone as
long as they share principle attributes (e.g., orientation, occupancy
schedule, lighting and equipment density, etc.)
2) IF you combine rooms into a single zone, you will lose reporting
capability for those rooms. You're trading simplicity and reduced
simulation time for detailed reporting. In my experience, there is
rarely a need to know the energy use for individual rooms. If, on the
other hand, you are trying to use E+ to get heating and cooling loads,
it may make sense to keep the rooms separated...
3) I have not modeled a system exactly as you describe, however it
sounds like you can model a simple air handler with heating or cooling
as desired and, for the zones, define a Direct Air object with the
correct airflow. Since Fan coils (I presume "fcu" is a fan coil unit)
are zone objects, you may also use these in concert with the air
handler, along with the proper zone control (i.e., thermostat and
scheduling)objects.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "drjonesg1958"
<drjonesg1958@...> wrote:
>
> Hi all I am new to simulation.
> Can some one explain
> 1. is it okay to combine multiple rooms with varying internal loads
> into one thermal zone (exposure of rooms is similar)
> 2. If acceptable, then how to get design loads / simulation results of
> individual rooms when they are clubbed into a zone
> 3. How to a model a system where individual rooms have a fcu and fresh
> air is supplied through are separate treated fresh air AHU to each fcu
> with no control.
>
> thanks
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/