[EnergyPlus_Support] Re: RUNS Question



Thanks Linda-
     Also, is there a way to copy objects between idf files? Thanks 
again.
              

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> 
wrote:
>
> You can run a free floating temperature run with no HVAC system 
set up:
> 
> see example file: 1ZoneUncontrolled.idf
> 
> If you want to size an HVAC system, I'd suggest looking at the 
> CompactHVAC example files.  These will set up all the branch/node 
> statements for you.
> 
> e.g.  CompactHVAC-5ZonePurchAir.idf
> 
> or any of the files starting with names CompactHVAC
> 
> or look at the example files which start "PurchAir".  these do 
> theoretical "loads" on a system but have no branches or nodes 
> explicit in the input file.  They do have thermostat settings, etc.
> 
> Or are you specifically trying to Size a system?  That's a 
different answer.
> 
> Linda
> 
> At 01:04 PM 8/8/2008, bluegreenearth13 wrote:
> >Could someone explain the difference between running the zone 
sizing
> >vs. system sizing vs. plant sizing runs? All I have in terms of
> >building information is the geometries and general zone settings
> >(cooling set point, RH) and I am having trouble setting up a full 
HVAC
> >system for the idf. Is one of the runs designed so that if I only 
set
> >up the ZONE SIZING it will still run without branch/node 
information?
> >  Thanks.
> >
> >
> >------------------------------------
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the 
> >appropriate folder in the Files area of the Support Web Site.
> >
> >EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
> >under the Documentation link and press the "search" button.
> >Yahoo! Groups Links
> >
> >
> >
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/