Re: [EnergyPlus_Support] LOW TEMP RADIANT SYSTEM shut-off



The purchased air is an independent way  to cool/heat the space. It
should not be used with other explicitly defined systems such as
radiant system. I do not agree to edit the weather file is a correct
way to do it. Actually, the weather file tell you that you cannot let
your radiant system on all the time. This will generate problems such
as condensation.

Bing

On 8/13/08, Florian Stift <florian.stift@xxxxxxxxx> wrote:
> Dear E+Users,
>
> I am simulating a single zone which is cooled by a "LOW TEMP RADIANT
> SYSTEM"!
> I wanted the system to be continuously "ON", so I defined a very low
> zone cooling setpoint, like 2degC.
>
> When I was realising that the system shuts off when condensation
> occurs on the inside of the ceiling surface, I added a Purchased Air
> System to serve the zone with a limited amount of conditioned air,
> e.g. 0,5ACH with 22deg.C.
>
> There is no condensation any more but the LOW TEMP RADIANT SYSTEM
> shuts off when the zone air temperature falls below that 22degC from
> the Purchased Air Schedule, but I still have defined that schedule for
> a Setpoint of 2degC.
>
> How can I manage to tell the LOW TEMP RADIANT SYSTEM to be ON all the
> time??
>
> Thanks in advance for any help!
>
> Best Wishes,
> Florian
>
>

------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/