[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Report Variable: Time Not Met Comfortable



Dear Bing,

Check p. 954 in the IO Reference: That report variable is keyed to the "People" object (occupancy) only when you use the variable "...Setpoint Not Met While Occupied", and it looks for instances where the room temp varies from the setpoint by more than .2C.

If you don't use the ".. While Occupied" version of the report variable, occupancy is not checked.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Bing Dong" <bingcat2007@...> wrote:
>
> Hi,
>
> Regarding to the Report Variable: Time Not Met Comfortable, does it
> dynamically links back to the occupancy schedule I specified, such as
> excluding the weekend for office building? I found even I got 0 hour
> for Time Not Met Setpoint (23 C), there is still 8 hours/week that not
> met comfortable.
>
> Thanks,
>
> Bing
>
__._,_.___

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___