Re: [EnergyPlus_Support] Re: enquires (URGANT)
You can only use 1 air loop per zone since you can have only 1 return
node. You should use the air primary loop to condition the outdoor and
and provide it to the zone. Then use a piece of zone equipment to
condition the remaining load in the zone see the WindACAuto example file).
lee_ching_hei wrote:
>
> I think one mixing box can only be connected in one system. Maybe u
> can establish 2 different single systems by adjusting the air flow
> rate - one for all outside air (100%)and one for the room air (with
> 0% of outside air).
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>, Sze Hung Lee
> <be074240@...> wrote:
> >
> > Dear Sir/Madam,
> >
> > ? There are two systems connected together to supply the air to the
> same zone, namely the CAV air condtioning system with fully outdoor
> air?and the CAV air conditoing system with?room air?return. How?is
> the system? constructed in the EnergyPlus file? ?
> >
> > For the detail,
> > I established two branches for the?cooling process.?The outdoor?air
> is?treated by??"CAV air condtioning system with fully outdoor air"?
> and the?returen air is treated by "CAV air conditoing system with?
> room air?return".?The?treated air after?these two?loop is then mixed
> by a?mixer box?in "plant-condenser flow control" and a duct is
> created as a branch loop for mixing. The same method has been done on
> outlet loop of zone oulet but use the spliter as for spliting the
> return air back into return air node.
> >
> > ? However, the serve statement as below was shown. Is it possible
> that a zone outlet connect to two return air branch inlet? Please
> help to solve the problem. I am urgant to establish this system. Look
> forward to your reply and please reply as soon as possible.
> >
> > Many thanks in advance.
> >
> >
> >
> > ?? ** Severe? ** Duplicate Node Name used for ZoneEquipGroup Outlet
> Node=RETURN AIR MIXER OUTLET
> > ?? **?? ~~~?? ** ...detected in Air Loop=VAV SYS 3
> > ?? **?? ~~~?? ** ...first used in Air Loop=VAV SYS 1 for
> ZoneEquipGroup Outlet Node
> > ?? ** Severe? ** Duplicate Node Name/List used for SupplyAirPath
> ZoneEquipGroup Inlet Nodes=ZONE EQ IN NODE 1
> > ?? **?? ~~~?? ** ...detected in Air Loop=VAV SYS 3
> > ?? **?? ~~~?? ** ...first used in Air Loop=VAV SYS 1 for
> SupplyAirPath ZoneEquipGroup Inlet Nodes
> >
> >
> > ?ºä?ä¸?æ–·??å?Yahoo! Mail,é??Žé?港è??€ä½ å??‡æ?見調?¥ã€
> ‚è???å?http://surveylink.yahoo.com/wix/p5429076.aspx
> <http://surveylink.yahoo.com/wix/p5429076.aspx> ?¼è¡¨ä½ ç???è?!
> >
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/