Airflow is nto explicitly related to geometry
except through some of the AirflowNetwork object, which use windows or virtual
geometry. To move air (air heat balance energy) between zones or outside,
you need to specify exactly how it will move, there are no objects that
automatically have airflow associated with them as in the real
world.
Try a simple Ventilation object first, there is a
wind sensitivity paramter available there. The ventilation object is
associated with a zone, not geometry. For more accurate calcs, use
AirflowNetwork. There are alot of example files to draw from.
David
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.