You are allowed only 1 mixer and zero splitters in the return air path.
Since return plenums like a mixer (multiple inlets, 1 outlet) and you
aren't allowed to
use splitters, the configuration you describe can't be modeled. You can
do something
like 4 zones => 2 return plenums => 1 return plenum, but there is
no way to "split"
the flow in the return air path.
Fred Buhl
nina.defreyne wrote:
Is it really possible for return plenums to be in parallel?
I'm modelling a system where the last two return plenums must be in
parallel, but it gives an error:
The air first goes to a splitter to 4 different zones, then the air
of the 4 zones goes to a return plenum. After that the air of this
return plenum has to go to 2 other return plenums (in parallel). I
have done that by placing a splitter after the first return plenum
and a mixer after te last two return plenums, but this doesn't seems
the right way because it gives an error about the splitter and mixer
inlet and outlet nodes. (I think it isn't possible to connect a
return plenum with a slitter or mixer in energy plus)
How is it possible to let the air split up to 2 return plenums? (and
to let it come together again)?
thanks,
Nina.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
Return plenums are much more flexible and may be in parallel or in
series. A return plenum can have multiple inlets and a single
outlet. The temperature impacts on the plenum zones are lagged by
one zone timestep for each level of plenum.
The return air flow must originate in a zone which has an air loop
supply inlet. This supply flow, less any exhaust from that zone,
establishes the return air flow rate. A return plenum can receive
one or more return flows (either directly from zones or from other
return plenums) and pass the total flow through it's outlet to
another plenum or to a zone mixer or to the air loop return inlet.
Mike
On 7 Aug 2003, at 23:57, kirbyschapman wrote:
Can one zone feed to other zones? In other words, can i force the
air
to flow through successive zones, as in from one end of a
building to
the other?
Thanks for the help.
Kirby
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
Only one supply plenum is allowed per air loop.
Mike
On 7 Aug 2003, at 20:09, kirbyschapman wrote:
Hello, Folks.
I'm attempting to use four separate supply plenums. The
caveat
is that
the first plenum serves a couple of zones, plus the second
plenum. The
second plenum serves one zone and the third plenum. Finally,
the
third
plenum serves a final zone.
In doing so, I used a splitter from Plenum 1 to feed the two
zones and
Plenum 2. Then another splitter from Plenum 2 to a zone and
plenum 3.
This didn't work, and in fact the program crashed (I only ran
it
with
the first two zones).
Is this the correct way to tackle a situation like this?
Thanks much
Kirby
------------------------ Yahoo! Groups Sponsor
---------------------~--> Buy Ink Cartridges or Refill Kits
for
Your
HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h
on
orders
$50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
--------------------------------------------------------------
---
----~
->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the
appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to
http://docs.yahoo.com/info/terms/
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@g...
------------------------ Yahoo! Groups Sponsor
---------------------~--> Buy Ink Cartridges or Refill Kits for
Your
HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on
orders
$50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
------------------------------------------------------------------
---~
->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the
appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to
http://docs.yahoo.com/info/terms/
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/
__._,_.___
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|