Re: [EnergyPlus_Support] Fan Coil Total Cooling
Not sure what you mean by "single zone fan coil simuulation with
purchased air".
Generally a fan coil can do cooling even though the cooling coil is off
- for instance
there may be some outside air mixed in with the recirculated air and the
resulting
mixed air may be below the room temperature.
Fred Buhl
Florian Stift wrote:
> Hi all,
>
> I'm confused about the results I'm getting for a single zone fan coil
> simulation with purchased air (FAN COIL UNIT:4 PIPE). I've set the
> thermostat to single heating setpoint, and can see that the zone
> temperature is free floating above the heating temperature. The Total
> Water Cooling Coil Rate is zero as expected. However, the Fan Coil
> Total Cooling Rate is not zero, but cycling for the whole year,
> averaging 400W. Shouldn't the Fan Coil Total Cooling Rate be zero?
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/