I think the statements in the Eng Ref are a little misleading. 1) In the HVAC calculation, the design volumetric flow rates are changed to design mass flow rates using a standard air density: StdBaroPress=101.325d0*(1.d0-2.25577D-05*Elevation)**5.2559d0 StdBaroPress=StdBaroPress*1000.d0 StdRhoAir=PsyRhoAirFnPbTdbW(StdBaroPress,constant_twenty,constant_zero) So the conditions are: a) elevation corrected standard barometric pressure; b) 20 C air temperature c) dry air (no moisture content) If Elevation = 0.0, then StdRhoAir = 1.294. Then all calculations are done in terms of mass flow rate. 2) in the envelope calculation, the density of air is calculated using the outside barometric pressure and the relevant air temperature and humidity ratio. For instance, in calculating interior surface convection coefficients, the current zone temperature and humidity ratio are used. Fred Buhl direzionecontraria wrote: Cz is on page 5. 1.204 kg/m3 is on pages 573 and 603. Regards Francesco --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Fred Buhl <wfbuhl@...> wrote: __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.