Fred:
We ran into this issue as well when completing RP865...where we saw different methods used
between BLAST and DOE-2...makes a small, but non-trivial difference. See the papers below for
more discussion:
Yuill, G., Haberl, J. 2006. "Accuracy Tests for Simulations for Single Zone, Two Pipe, Four Pipe and Induction Air Handling Systems " ASHRAE Transactions-Research, Vol. 112, Pt. 1, (January).
Yuill, G., Haberl, J. 2005. "Accuracy Tests for Simulations of Constant Volume, Dual Duct and Variable Volume Air Handling Systems (4796)," ASHRAE Transactions-Research, Vol. 111, Pt. 2, pp. 137-153, (June).
Jeff
8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) :=') 8=) 8=) 8=?
Jeff S. Haberl, Ph.D., P.E.............................jhaberl@xxxxxxxxxxxx
Professor......................................................Office Ph: 979-845-6507
Department of Architecture.......................Lab Ph: 979-845-6065
Energy Systems Laboratory.......................FAX: 979-862-2457
Texas A&M University..............................77843-3581
College Station, Texas, USA.......................URL: www-esl.tamu.edu
8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) 8=? 8=) 8=) 8=)
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx on behalf of Fred Buhl
Sent: Fri 2/6/2009 2:30 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Re: air density in the heat balance
I think the statements in the Eng Ref are a little misleading.
1) In the HVAC calculation, the design volumetric flow rates are changed to
design mass flow rates using a standard air density:
StdBaroPress=101.325d0*(1.d0-2.25577D-05*Elevation)**5.2559d0
StdBaroPress=StdBaroPress*1000.d0
StdRhoAir=PsyRhoAirFnPbTdbW(StdBaroPress,constant_twenty,constant_zero)
So the conditions are: a) elevation corrected standard barometric pressure; b) 20 C air temperature
c) dry air (no moisture content)
If Elevation = 0.0, then StdRhoAir = 1.294.
Then all calculations are done in terms of mass flow rate.
2) in the envelope calculation, the density of air is calculated using the outside barometric
pressure and the relevant air temperature and humidity ratio. For instance, in calculating
interior surface convection coefficients, the current zone temperature and humidity ratio
are used.
Fred Buhl
direzionecontraria wrote:
Cz is on page 5.
1.204 kg/m3 is on pages 573 and 603.
Regards
Francesco
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx> , Fred Buhl <wfbuhl@...> <mailto:wfbuhl@...>
wrote:
Could you tell us what section or page of the Engineering
Reference you
are looking at?
Fred Buhl
direzionecontraria wrote:
Hello!
I refer to "Engineering Reference"
http://apps1.eere.energy.gov/buildings/energyplus/pdfs/engineeringref <http://apps1.eere.energy.gov/buildings/energyplus/pdfs/engineeringref>
ere
nce.pdf
In the equations of the heat balance on the zone, for example in
the
equation (2), there is the term Cz, which is the air capacitance.
Cz = (air density )*(volume of the zone)
I read that the standard air density is 1.204 kg/m3.
What are the standard conditions ? How is the air density
calculate in
different conditions from the standard conditions?
With Regards
Francesco
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov <http://www.energyplus.gov/>
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/ <http://groups.yahoo.com/group/EnergyPlus_Support/>
Attachments are not allowed -- please post any files to the
appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the Documentation link and press the "search" button.
Yahoo! Groups Links
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov <http://www.energyplus.gov/>
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/ <http://groups.yahoo.com/group/EnergyPlus_Support/>
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/