Astrid:

My answers will follow your questions.

> control mode "temperature", and as far as I understood it, the
> settings at "airflownetwork:multizone:zone" define the window opening
> percentage in relation to the temperature difference, right?

A: Your understand is correct.

> the settings in "airflownetwork:multizone:component detailed opening"
> opening factor 1 defines the smallest opening angle/width and 4 the
> largest, correct?

A: Yet, it is correct. The largest number is determined by the number you 
enter in the Number of sets of Opening Factor Data field. The maximum is 4 
and the minimum is 2.

> largest, correct? So "airflownetwork:multizone:zone" defines, how the
> opening percentage varies in between. But what effect do opening
> factor 2 and 3 have in this case?

The opening factor is calculated based on given conditions in either 
airflownetwork:multizone:zone or airflownetwork:multizone:Surface. Then the 
opening factor is used in a subroutine to deal with the 
AirflowNetwork:Multizone:Component:DetailedOpening object. The subroutine 
first checks two sets of opening factor data to make  "the opening factor i 
<= opening factor <= the opening factor i+1". For example, the opening 
factor 1 is 0, opening factor 2 is 0.2, and opening factor 3 is 1.0. The 
calculated opening factor is 0.6. Therefore, it is located between factor 
data sets 2 (0.2) and 3 (1.0). Then other values of discharge coefficient, 
...., will be linearly interpolated between data sets 2 and 3. Detailed 
description is given in the Group Airflow Network in the InputOutput 
Reference.

> What I want to do is, using a different maximum opening angle of the
> window in summer and in winter, so I was hoping this would be possible
> by using an additional opening factor...
> Hope this explains my question better?

You can not change any values defined in the 
AirflowNetwork:Multizone:Component:DetailedOpening objects during time. 
However, you can change schedule values defined in the Ventilation Control 
Zone Temperature Setpoint Schedule Name field in either 
airflownetwork:multizone:zone or airflownetwork:multizone:Surface to meet 
your needs.

Please let me know if you need more information.

Thanks.

Lixing


----- Original Message ----- 
From: "astrid.roetzel" <astrid.roetzel@xxxxxxxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Thursday, February 12, 2009 6:41 AM
Subject: [EnergyPlus_Support] Re: opening factors and ventilation control 
mode


> Dear Lixing,
>
> Thank you very much for the quick answer! I am using ventilation
> control mode "temperature", and as far as I understood it, the
> settings at "airflownetwork:multizone:zone" define the window opening
> percentage in relation to the temperature difference, right? And in
> the settings in "airflownetwork:multizone:component detailed opening"
> opening factor 1 defines the smallest opening angle/width and 4 the
> largest, correct? So "airflownetwork:multizone:zone" defines, how the
> opening percentage varies in between. But what effect do opening
> factor 2 and 3 have in this case?
> What I want to do is, using a different maximum opening angle of the
> window in summer and in winter, so I was hoping this would be possible
> by using an additional opening factor...
> Hope this explains my question better?
>
> Astrid
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>>
>> Astrid:
>>
>> Could you provide specific information on names of field and object
> related
>> to more than two opening factors?
>>
>> Best regards,
>>
>> Lixing
>>
>> ----- Original Message ----- 
>> From: "astrid.roetzel" <astrid.roetzel@...>
>> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
>> Sent: Wednesday, February 11, 2009 3:22 PM
>> Subject: [EnergyPlus_Support] opening factors and ventilation
> control mode
>>
>>
>> > Dear experts,
>> >
>> > I am not sure if I understood correctly, how the ventilation control
>> > mode interacts with the opening factors if there are more than two of
>> > them. Can anyone help me?
>> > Thanks a lot,
>> >
>> > Astrid
>> >
>> >
>> >
>> > ------------------------------------
>> >
>> > The primary EnergyPlus web site is found at:
>> > http://www.energyplus.gov
>> >
>> > The group web site is:
>> > http://groups.yahoo.com/group/EnergyPlus_Support/
>> >
>> > Attachments are not allowed -- please post any files to the
> appropriate
>> > folder in the Files area of the Support Web Site.
>> >
>> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf
> under the
>> > Documentation link and press the "search" button.
>> > Yahoo! Groups Links
>> >
>> >
>> >
>> >
>>
>
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate 
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the 
> Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
> 



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/