[EnergyPlus_Support] Re: is it possible to model 2 air loops
Hello,
I tried to connect the loops as you suggest but it does not seem to
work the way I want it: I would like to have the possibility that the
main loop has two outside air nodes: one representing the real outside
air (fresh air) and the second one representing the outlet air node of
the other loop. Somehow I should need an additional inlet node on the
Heat Recovery Unit or in the Mixing Box.
Any other suggestions?
Tks,
Santiago
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> I have not tried that. You will probably have to delete the Outside Air
> Node List object for the 1st mixing box OA node. And the OA flow rate
> leaving the relief node of one box should be the same as the OA inlet
> node flow rate on the 1st box.
>
> Let me know what happens.
>
> Elreq wrote:
> >
> >
> > Hello!
> >
> > I finally managed to work it out. Now I have the two loops but I
> > wonder if there is a way to connect the relief outlet of one of them
> > to the mixing box of the 1st one.
> >
> > The other option would be to use a mixing object but is not what the
> > real situation.
> >
> > Thanks in advance.
> > Santiago
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > Is that node name used in the OutdoorAir:Mixer object ? If you can't
> > > find the error you will have to upload your file so someone can
take a
> > > look at it.
> > >
> > > Elreq wrote:
> > > >
> > > > This node is defined in an outisde air node list:
> > > >
> > > > OUTSIDE AIR INLET NODE LIST,
> > > > AHU Outside Air Inlet; !- 1st Node name or node list name
> > > >
> > > > Regards,
> > > > Santiago
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > > <RRaustad@> wrote:
> > > > >
> > > > > Did you define this node as an outdoor air node or list this
> > node in an
> > > > > outdoor air node list ?
> > > > >
> > > > > OutdoorAir:Node,
> > > > > AHU OUTSIDE AIR INLET; !- Name
> > > > >
> > > > > ...or...
> > > > >
> > > > > OutdoorAir:NodeList,
> > > > > OutsideAirInletNodes; !- Node or NodeList Name 1
> > > > >
> > > > > NodeList,
> > > > > OutsideAirInletNodes, !- Name
> > > > > AHU OUTSIDE AIR INLET; !- Node 1 Name
> > > > >
> > > > >
> > > > > Elreq wrote:
> > > > > >
> > > > > > The error is:
> > > > > > Node Connection Error, Node="AHU OUTSIDE AIR INLET", Actuator
> > node did
> > > > > > not find a matching node of appropriate type (other than
Actuator,
> > > > > > Sensor, OutsideAir).
> > > > > > ** ~~~ ** Reference Object=CONTROLLER:OUTSIDE AIR, Name=AHU OA
> > > > > > CONTROLLER.
> > > > > >
> > > > > > This controller is for the AHU Loop which was alreay working
> > fine so
> > > > > > when I added the second loop for a special zone I receive this
> > error.
> > > > > >
> > > > > > Thanks.
> > > > > >
> > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > > > > <RRaustad@> wrote:
> > > > > > >
> > > > > > > Yes, you may use more than one air loop. Each air loop must
> > serve
> > > > > > > different zones. What is the strange error ?
> > > > > > >
> > > > > > > Elreq wrote:
> > > > > > > >
> > > > > > > >
> > > > > > > > Dear Forum,
> > > > > > > >
> > > > > > > > I have a similar question,
> > > > > > > >
> > > > > > > > Is it possible to define two air loops but not for the
same
> > > > zone: one
> > > > > > > > is for several zones and has reheat coils and the
other one is
> > > > for a
> > > > > > > > separate zone only using direct air.
> > > > > > > >
> > > > > > > > I am trying to do it but receive very strange severe
errors.
> > > > > > > >
> > > > > > > > Thanks,
> > > > > > > > Santiago
> > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Fred Buhl
> > <wfbuhl@>
> > > > > > > > wrote:
> > > > > > > > >
> > > > > > > > > It is not possible. One airloop, plus as much zone
equipment
> > > > as you
> > > > > > > > want.
> > > > > > > > >
> > > > > > > > > Fred Buhl
> > > > > > > > >
> > > > > > > > > D T wrote:
> > > > > > > > > > Does anyone know if it possible to have 2 air loops
> > > > servicing the
> > > > > > > > same
> > > > > > > > > > zone? I currently have one air loop defined for the
> > > > largest zone
> > > > > > > > in my
> > > > > > > > > > facility and am trying to add another one but am
trying to
> > > > > > figure out
> > > > > > > > > > how to connect the nodes on the demand side since
that is
> > > > where my
> > > > > > > > > > problem lies.
> > > > > > > > > >
> > > > > > > > > > Thanks,
> > > > > > > > > > Dimos
> > > > > > > > > >
> > > > > > > > > >
> > > > > > > > > >
> > > > > > > > >
> > > > > > > >
> > > > > > > >
> > > > > > >
> > > > > > > --
> > > > > > > Richard A. Raustad
> > > > > > > Senior Research Engineer
> > > > > > > Florida Solar Energy Center
> > > > > > > University of Central Florida
> > > > > > > 1679 Clearlake Road
> > > > > > > Cocoa, FL 32922-5703
> > > > > > > Phone: (321) 638-1454
> > > > > > > Fax: (321) 638-1439 or 1010
> > > > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > > >
> > > > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > > > >
> > > > > >
> > > > > >
> > > > >
> > > > > --
> > > > > Richard A. Raustad
> > > > > Senior Research Engineer
> > > > > Florida Solar Energy Center
> > > > > University of Central Florida
> > > > > 1679 Clearlake Road
> > > > > Cocoa, FL 32922-5703
> > > > > Phone: (321) 638-1454
> > > > > Fax: (321) 638-1439 or 1010
> > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > >
> > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > >
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
<http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/