[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Air flow from one zone to another: extraction to return air duct
While trying to implement your suggestion, I found another problem:
For the first zone, I defined an AirTerminal:SingleDuct:VAV:Reheat and
this object is than used in a new ZoneHVAC:AirDistribution unit. I
made the ZoneHVAC:EquipmentList (also including an exhaust fan) and
next the ZoneHVAC:EquipmentConnections. For zone 1, I've defined an
inlet node list, an exhaust node and a return air node (I've connected
the return air node to my ZoneMixer).
Then for zone 2, I was planning to use the outlet air node of the zone
1 exhaust fan as the zone 2 inlet air node. However: I can't define a
ZoneHVAC:EquipmentConnections object without first defining a
ZoneHVAC:AirDistributionUnit for zone 2. As I've told you: there
actually is no conditioned air distributed in zone 2, so this is a new
problem.
Again, thank you for your help.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> No, do not use a new AirTerminal. Just define an inlet and exhaust
node
> name for zone 2 and an inlet node name for zone 3 the same way you
did
> for zone 1.The name of the inlet node in zone 2 is the same as the
> exhaust fan outlet node name from zone 1. Use the exhaust node name
from
> zone 2 as the exhaust fan inlet node name and the inlet node name in
> zone 3 as the exhaust fan outlet node name for the exhaust fan that
> connects zone 2 and 3.. Yes, the node names define the connection.
> Again, I'm not sure this will work, but I can't think of anything
else
> other than deleting the exhaust fan in zone 1 and using the RA from
zone
> 1 to increase the flow through the HX. If you choose to delete the
> exhaust fan in zone 1, ignore the warning of flow imbalance in zone
1.
> Make sure you check the RA, SA, and EA flow rates in zone 1, 2 and 3
no
> matter which method you use.
>
> ZoneHVAC:EquipmentConnections,
> RESISTIVE ZONE, !- Zone Name
> Zone1Equipment, !- Zone Conditioning Equipment List
Name
> Zone1Inlets, !- Zone Air Inlet Node or NodeList Name
> , !- Zone Air Exhaust Node or NodeList
Name
> Zone 1 Node, !- Zone Air Node Name
> Zone 1 Outlet Node; !- Zone Return Air Node Name
>
> NodeList,
> Zone1Inlets, !- Name
> Zone 1 Inlet Node; !- Node 1 Name
>
>
> joskenzy wrote:
> >
> > This is probably not a smart question, but I am new to EnergyPlus
so
> > forgive me for
> > asking: how can i connect the outlet node of an exhaust fan to a
zone
> > node?
> >
> > I am not using the AirflowNetwork, so I don't have air
distribution
> > nodes in my zones...
> > Do you mean I have to define a new
> > AirTerminal(SingleDuct:Uncontrolled), and use the
> > outlet node of the exhaust fan as the air inlet node of this
> > AirTerminal-object? I thought
> > this was just a matter of giving nodes a name, I didn't think they
> > were connected just by
> > using the same name?
> >
> > Thanks again..
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > Yes, that would be thermally incorrect, but at least you would
have the
> > > air balance on the RA nodes. You just want to get as close as
possible
> > > with the tools you have available. The only other thing I can
think of
> > > is to use a zone exhaust in zone 1 and connect the exhaust fan
outlet
> > > node to an inlet node in zone 2, and the zone exhaust fan outlet
from
> > > zone 2 to an inlet node in zone 3. I have tried this before but
can't
> > > recall what happened. If that works, you would not have to use
the
> > > mixing objects. There would of course be fan heat involved in
moving
> > the
> > > air so adjust the fan power down as far as you can go.
> > >
> > > joskenzy wrote:
> > > >
> > > > There is no RA flow rate in zone 1, because I use a
> > Fan:ZoneExhaust in
> > > > this zone. By doing
> > > > so, the flow balance in zone 1 is correct.
> > > >
> > > > To keep things simple, I first wanted to delete the
> > Fan:ZoneExhaust in
> > > > zone 1 and use the
> > > > corresponding RA flow rate from this zone in the return duct,
but
> > this
> > > > is thermally
> > > > incorrect: the air passing from zone 1 first heats zone 2 and
then
> > the
> > > > air from zone 2
> > > > heats zone 3: the RA from zone 3 will be cooler than the RA
from
> > zone 1..
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > > <RRaustad@> wrote:
> > > > >
> > > > > Wait a minute, if the air from zone 1 is moved to zone 2 and
3 using
> > > > > mixing objects, isn't there a RA flow rate on zone 1
already?
> > > > >
> > > > > Richard Raustad wrote:
> > > > > >
> > > > > > How about trying to connect the outlet node of the
> > Fan:ZoneExhaust
> > > > to a
> > > > > > new inlet node in zone 1 (and disregard the flow imbalance
> > warnings in
> > > > > > zone 3). Does this give you a RA flow rate in zone 1?
> > > > > >
> > > > > > joskenzy wrote:
> > > > > > >
> > > > > > >
> > > > > > > No I haven't, but I don't really see how this could
solve my
> > > > problem:
> > > > > > >
> > > > > > > 1) If I use a Fan:ZoneExhaust in zone 3, the air flow
balance
> > > > for this
> > > > > > > zone will fail (there is
> > > > > > > no supply air, no return air, only exhaust air) ? I
believe
> > > > ZoneMixing
> > > > > > > is not taken into
> > > > > > > account in the air flow balance?
> > > > > > >
> > > > > > > 2) If I connect the Fan:ZoneExhaust in zone 3 to the air
inlet
> > > > node of
> > > > > > > my heat exhanger
> > > > > > > (HeatExchanger:Dessicant:BalancedFlow), than I cannot
> > connect the
> > > > > > > return air duct of the
> > > > > > > other zones (there are 14 other VAV-zones in my
building,
> > apart from
> > > > > > > the 3 zones
> > > > > > > considered in my example) to this HX ?
> > > > > > >
> > > > > > > Thank you anyway, I appreciate your effort!
> > > > > > >
> > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard
Raustad
> > > > > > > <RRaustad@> wrote:
> > > > > > > >
> > > > > > > > Have you tried connecting the outlet of the
> > Fan:ZoneExhaust in
> > > > zone
> > > > > > > 3 to
> > > > > > > > the heat exchanger ?
> > > > > > > >
> > > > > > > > joskenzy wrote:
> > > > > > > > >
> > > > > > > > > Could anyone help me implement the following
ventilation
> > > > concept:
> > > > > > > > >
> > > > > > > > > Say the building has 3 zones: treated air
> > > > (SingleDuct:VAV:Reheat) is
> > > > > > > > > injected in the first zone. The same air flow rate
passes
> > > > from the
> > > > > > > > > first, through the second and into the third zone.
> > > > > > > > >
> > > > > > > > > There is no treated air injected in the second or
the third
> > > > zone.
> > > > > > > > >
> > > > > > > > > An air flow rate equal to the injection rate in zone
1 is
> > > > extracted
> > > > > > > > > from zone 3.
> > > > > > > > >
> > > > > > > > > Normally, one would suggest to supply air to zone 1
and
> > to use a
> > > > > > > > > Fan:ZoneExhaust to balance air flows. Using
ZoneMixing,
> > you can
> > > > > > > > > simulate air flowing from zone 1 to zone 2, and air
flowing
> > > > from
> > > > > > zone
> > > > > > > > > 2 to zone 3.
> > > > > > > > >
> > > > > > > > > However (now comes the hard part): the building has
other
> > > > > > VAV-balanced
> > > > > > > > > zones, and I want to add the extracted air from zone
3 to
> > > > the return
> > > > > > > > > duct of the other zones because the return air is
used in a
> > > > heat-
> > > > > > > > > exchanger.
> > > > > > > > >
> > > > > > > > > So for zone 3, I have an air flow entering the zone
because
> > > > of the
> > > > > > > > > ZoneMixing (zone 2 as source zone), but how can I
add the
> > > > replaced
> > > > > > > > > zone air to the air in the return duct?
> > > > > > > > >
> > > > > > > > > I looked at the manual and at previous topics here,
but I
> > > > only found
> > > > > > > > > that ZoneMixing adds air to a zone, while supposing
an equal
> > > > > > flow rate
> > > > > > > > > has left the zone (without knowing where the air
went)..
> > > > > > > > >
> > > > > > > > > I would really appreciate your help!
> > > > > > > > >
> > > > > > > > >
> > > > > > > >
> > > > > > > > --
> > > > > > > > Richard A. Raustad
> > > > > > > > Senior Research Engineer
> > > > > > > > Florida Solar Energy Center
> > > > > > > > University of Central Florida
> > > > > > > > 1679 Clearlake Road
> > > > > > > > Cocoa, FL 32922-5703
> > > > > > > > Phone: (321) 638-1454
> > > > > > > > Fax: (321) 638-1439 or 1010
> > > > > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>>
> > > > > > > >
> > > > > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > > > > >
> > > > > > >
> > > > > > >
> > > > > >
> > > > > > --
> > > > > > Richard A. Raustad
> > > > > > Senior Research Engineer
> > > > > > Florida Solar Energy Center
> > > > > > University of Central Florida
> > > > > > 1679 Clearlake Road
> > > > > > Cocoa, FL 32922-5703
> > > > > > Phone: (321) 638-1454
> > > > > > Fax: (321) 638-1439 or 1010
> > > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> > > > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>>
> > > > > >
> > > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > > >
> > > > > >
> > > > >
> > > > > --
> > > > > Richard A. Raustad
> > > > > Senior Research Engineer
> > > > > Florida Solar Energy Center
> > > > > University of Central Florida
> > > > > 1679 Clearlake Road
> > > > > Cocoa, FL 32922-5703
> > > > > Phone: (321) 638-1454
> > > > > Fax: (321) 638-1439 or 1010
> > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu> <http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>>
> > > > >
> > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > >
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
<http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/